Mattja

-
Reaction score
10
The full blurb is below, but the TLDR is: RCD that tested perfectly (ramp test to 27mA can't remember the numbers for trip times but all was good), nothing I can find that would be causing the tripping, someone replaced the RCD with an apparently identical one and the tripping stops... I'm confused by this.


The full story in all its boring detail:

RCD at a customers house would trip out at random times, several times per day. Testing the RCD it seemed to be working perfectly, 27mA on the ramp test and I can't remember exactly what the other numbers were, but all good.

As one of the socket circuits had tripped the mcb once I figured that's probably the problem circuit, so I set about the usual tests, find no insulation problem with the circuit (although I did find it had a broken line ring so I found and fixed that), and found no insulation problems with any of the equipment plugged in on that circuit either. While looking for the broken line I stumbled across a fused spur behind which the cpc had come out and was hovering close to the line terminal, no visible sign of arcing/contact but I make a mental note of "maybe this is the problem?"

I then, with the MS and RCD off and the mcbs on, connected the busbar and neutrals and insulation tested again, with all equipment that would normally be plugged in connected (at 250V only to ensure nothing gets damaged). The total result was about 0.1Mohm (almost instantly went up over 1Mohm and further, but that's the cold reading the moment the test started), and remember this is with all equipment plugged in before you're alarmed by that low reading. Anyway the leakage on that should be 240V/0.1 to 0.13 Mohm is about 2mA... at tops a tenth of the RCD trip current.

We'd already ruled out it being any particular item being plugged in/turned on manually, so my thoughts at this stage are that it's a piece of equipment that decides of its own when to become active, such as the fridge/freezer/boiler/immersion heater. So I force the fridge/freezer on using the quick-cool or w/e you call it buttons, no trip. Then turn off the boiler+immersion heater circuit with everything else on and go around looking for any equipment they may plug in that wasn't in when I checked the IR. When I'm out of anything I can think to check it hasn't tripped off, so I advise that they keep the boiler+immersion heater circuit off and if the tripping stops get the boiler checked out.

Of course it does trip again. At this point I advise that they try turning the circuits off one at a time and keeping each one off until either the RCD trips or the tripping appears to have stopped and keep a record of it, then I'd at least have a clue where to look for the problem, and perhaps put the guilty circuit into an RCBO instead if the problem can't be found.



Anyway after not hearing from them for a while I call and am told that another electrician simply replaced the RCD with one that I'm told is identical (at least that's what they told the homeowner, not sure the homeowner would be able to tell if it wasn't, I tried asking if it says 100mA instead of 30mA and they got a bit confused so I didn't press the issue). The tripping has apparently stopped... but you may recall from the start of this ramble that the RCD is the first thing I checked and it tested perfectly!


Does anyone have any idea what could be causing an RCD that tests well to nuisance trip? Or what else may be going on? Or am I right to wonder if the other guy put in a 100mA RCD?
 
I would possibly expect that the RCD was becoming oversensitive possibly being affected by voltage transients from installed equipment and that the fault current is hovering near the 30mA threshold, the new RCD may be just fractionally less sensitive and if there is a very short duration fault the RCD may not be tripping before the fault clears and so will have "resolved" the problem for a short while.
 
I would possibly expect that the RCD was becoming oversensitive possibly being affected by voltage transients from installed equipment and that the fault current is hovering near the 30mA threshold, the new RCD may be just fractionally less sensitive and if there is a very short duration fault the RCD may not be tripping before the fault clears and so will have "resolved" the problem for a short while
the possible fault n/earth or appliance /ext leads .
 
To be absolutely honest,you may only have the story from a customer who has used another spark,and they may be straight,but the second spark is wrong/lucky/imaginary,etc

Why did the customer use another spark? Definitely not suggesting owt sinister:) but,sometimes these type of fault chases,go on for months or years,with subsequent extra problems being cured/added,and luck or circumstances,altering outcome and results.

If it cheers you up,there are a host of electrical fault poltergeists,in properties,up and down the land...and some will only ever be tackled,found and solved,when the property is moved on to an owner, with a fresh attitude :)
 
Cheers guys, admittedly I didn't have a clamp meter with me so good chance you're right and the new RCD only trips right up at 30mA... Bit surprising since the old one got to 27mA on the ramp test (hence I didn't consider it too sensitive), but if an extra 3mA makes the difference so be it. Honestly I was wondering if someone would come out with some idea I'd not even considered and make a (slightly wiser) fool out of me!

@PEG I think the customer tried another spark hoping that they'd be able to find something I hadn't, which is fair enough with it still tripping out.
 

Reply to Confused about an RCD issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock