Hi, Ive been asked to connect up a site hoist and Ive never done one before, Its controlled by a 110v transformer, 5 KVA. Im calculating the cable size and am confused as to weather I should use 110 or 230 for the calculation, im pretty sure its 110 but I just wanna check as its a difference of about 25 amps, thanks in advance for any replies.
 
are you calculating from supply to tranny or tranny to hoist?
 
You ignore the secondary side then and calculate the primary demand .... when you transform down to 110v from 230v the voltage drops by half so the current will double (approx) on the 110v side. Whichever side has the highest voltage of a transformer will have the lowest current and this will be proportionate to the ratio of primary and secondary windings.
 
ah ok, so I calculate at 230 thanks, that'll save me a few quid, I was thinking that it was using 5KVA at 110v so would be drawing the higher current, thanks
 
ah ok, so I calculate at 230 thanks, that'll save me a few quid, I was thinking that it was using 5KVA at 110v so would be drawing the higher current, thanks

Remember Ohms law - power stays the same from input to output (minus losses). And V x I gives power. Daz
 
A 5KVA 1ph 230v transformer would be approx 21-22amp primary ....

Your issue here is your protective device you use ...if a BS60898 then inrush is a big issue and to guarantee trip free use then you would need either a 63 (b) or a 32 (d) checking your zs complies so be cautious to cable sizing ... can we assume you already have overload protection in place for the loads?
 
A 5KVA 1ph 230v transformer would be approx 21-22amp primary ....

Your issue here is your protective device you use ...if a BS60898 then inrush is a big issue and to guarantee trip free use then you would need either a 63 (b) or a 32 (d) checking your zs complies so be cautious to cable sizing ... can we assume you already have overload protection in place for the loads?

I was thinking of a 32 c?
 
so Zs needs to be max. 0.72. for a C32, you need to ensure that it's compliant, maybe up sizing the cable accordingly.
 
My recommendation comes from manufacturers guides they guarantee trip free on inrush ...some LV/LV transformers can peak inrush 20-25 times rated current although usually 10 -15 times if you fit a 32 (c) it may well give good service trip free but their again you may get occasional or frequent tripping its a hard call when you go outside the manufacturers guides... if you have a spare mcb that rating try it and explain to customer it may trip and if so you will order the correct size... this way you pre-rmpt the issue and don't loose face..... you could always fit other fuse types instead.
 
Zs for a 32A type D is 0.36. depending on your Zdb, you might have a struggle.
 
Yes following tels advice get the Zdb then you can calculate the cable resistance and estimate zs before you wire it ... a larger cable may be needed if supply is good enough to start with.... alternately you can protect with hrc fusing which is not so harsh regarding zs values ..... if you don't pre-empt this before hand you may find your installs doesn't comply so heads up ... If you have a TNCS system and a good reading you may get away with a 6mm but still calc it ...next cable size up should cover you if its too close to call.
 
Yes following tels advice get the Zdb then you can calculate the cable resistance and estimate zs before you wire it ... a larger cable may be needed if supply is good enough to start with.... alternately you can protect with hrc fusing which is not so harsh regarding zs values ..... if you don't pre-empt this before hand you may find your installs doesn't comply so heads up ... If you have a TNCS system and a good reading you may get away with a 6mm but still calc it ...next cable size up should cover you if its too close to call.

ok, maybe ill look into the hrc fuses, thanks
 
Update: Board Zs is 0.39! So that's type D out the window, at the mo I think its gotta be 32 type c, I don't really want unwanted tripping, Darkwood, where did you find the information you mentioned earlier about the MF's?
 

Reply to Connecting up site hoist. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Like a host of UK residents recently (230% increase in genny sales apparently), I've just invested in a small (3500W) portable, dual fuel...
Replies
12
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello everyone, I really hope this isn't an idiot question but boy, I'm out of my depth! I've spent about 3 weeks (not solid mind) trying to work...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock