Hi all
for a straight consumer change with out new circuits being added am i right in saying that you pir the installation then pirs are not notifiable hence no building controle !!!! only asked as thats what it seems says in gn3
thanks
Rich
 
Hey tucker.

For a c.u change you would need to use an EIC, not PIR.

ON the EIC you just fill in what you have done in the extent covered box, i.e upgrading of consumer unit and bonding etc. Then test all circuits as normal.

Cheers
 
What he said^^^, however, you should put right any major deviations ie lack of main bonding etc.

I always carry out a PIR prior to a CU change because you never know what nasties may be lurking that may catch you out.
 
What he said^^^, however, you should put right any major deviations ie lack of main bonding etc.

I always carry out a PIR prior to a CU change because you never know what nasties may be lurking that may catch you out.
surely this adds more cost to the customer , what i do is explain what problems could occur ie new 17th board could start tripping or no ring continuity and put in writing any of this extra work would have to be carried out on a ttime and materials basis then your covered when all the nasties pop .
 
Indeed, but, as i said, any major deviations need rectifying as well.

Have always explained this to the customer and never had one turned down yet.

Especially if the install looks like its been altered or is reasonably old.
 
Indeed, but, as i said, any major deviations need rectifying as well.

Have always explained this to the customer and never had one turned down yet.

Especially if the install looks like its been altered or is reasonably old.
its a good point id say both ways work just as well, as in my case estimate to install bonding and replace c.u, inform client you would then carry out a test on the whole of the installation and issue a report of its condition with an estimate for cost of repairs if any .
 

Reply to consumer exchange pir/eic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
881
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
994
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
484
NICEIC Certification Scheme SPD on old consumer unit?
Under amendment 2 of the BS7671, there is now a requirement to fit an SPD as standard. I am due to install a new outdoor socket circuit on an...
Replies
2
Views
1K
Hi all. Customer asking me to fix 3 phase consumer unit on a new shop . Its brand new installation . He want to use every part of shops and he...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock