Discuss Consumer Unit isolator with RCD in the DIY Electrical Advice area at ElectriciansForums.net
I have an old CU with BS3036 rewireable fuses. I'm having the board upgraded soon but in the meantime I'd like to add RCD protection. Can anyone tell me where I can find a consumer unit isolation switch with RCD built in - to fit between the meter and the CU?
Just upgrade the CU, the cost to add an upfront RCD and the potential problems and inconvenience it could cause are not worth the expense. Also when the CU is upgraded the RCD will be redundant so it is more cost effective to put the cost of the upfront RCD into the new CU from the start
To add to the above if you have not had it tested the addition of a main rcd switch may just result in unwanted tripping if there are underlying faults.
Reactions: DPG
It was a good few years ago now, but one of my customers ended up dead because I took this approach.
Thanks for the reply. What happened to cause the fatality?
The belt had come off in their washing machine. She was knelt behind it, with the back off, guiding the belt back on, while he turned the drum from the front. Heater element terminals are just below the drum pulley, and, for reasons I've never worked out, tend to be switched on the neutral side, so are both live whenever the machine is switched on.
She must have touched one of the terminals, and was found dead in a kneeling position behind the machine, when her partner realised she was not responding to him.
Rewiring, with new RCD protected consumer unit, was due to start in a couple of weeks time.
How awful, just shows how easy it can happen. Thanks for explaining that.
When most 3036 boards only have 4 - 6 ways a new CU with 4 - 6 RCBO's would not be that much more expensive than an upfront RCD ok the installation of a new CU would be a little bit more expensive but I believe that is what most electricians would recommend and not just because of making a little bit more on the job
So there were some mitigating circumstances that resulted in this tragic death not least the safe isolation of the washing machine
So are you saying that you would have installed the upfront RCD sooner than what appears to be the scheduled upgrade of the CU thus possibly preventing this tragedy
Reply to Consumer Unit isolator with RCD in the DIY Electrical Advice area at ElectriciansForums.net
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
HI My flat just failed the EICR because there is no RCD in the consumer unit. There is no space for a new RCD as the consumer unit is full. Do I...
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...