- Reaction score
- 17,014
as the job is temporary and the house load will not even exceed 80 amps let alone 100amps do you think it would be fine to connect a 16mm cable from the meter to the vonsumer unit even if the dno use 25mm tails or shall I use a 25mm cable too
Whether it is temporary or not it needs to be carried out in accordance with bs7671 including initial verification.
It won't be fine to connect a cable directly from the meter to the CU, if the length is 7 metres, regardless of what size it is.