Hello, I’m need some advice on how a contactor is wired please and where the neutral go. I’m told it is connected to eco 7 and controls 3 heaters in a domestic flat. It stopped working after an electrician did something on a different circuit in the consumer unit.

The contactor is an Eaton cr2540230.

At the moment there is 3 lives coming from 3 MCB’s and they go into the bottom of the contactor in terminals 2,4 and 6.

Then 3 lives feed the heaters from the top of the contactor in terminals 1,3 and 5.

The neutral from the N bar is connected to A2 and the outgoing N is connected in terminal 7(13).

There is noting in A1.

Does this sound correct?

I’ve added a photo.

Thanks41D750D1-754D-452E-9BA5-9E1BCB9EA7ED.jpeg
 
Last edited by a moderator:
I doubt that is an 'outgoing' neutral, its probably the switched live from the controller which should go to A1
So your saying the switched live in to A1, the neutral in to A2 and the 3 live in at the bottom and out at the top?
 

Attachments

  • 0649B8ED-7F71-43C7-83B7-1F609EF052F1.jpeg
    316.5 KB · Views: 20
  • BF5B2A9D-9A90-49B5-B6EC-7BCCE4DFE108.jpeg
    268.2 KB · Views: 20
Or 3 live in the top, and out at the bottom.

Definitely needs a live and neutral across A1-A2 to pull the coil in.

1-2, 3-4 and 5-6 are just normally open switches.
 
7-8 will be the same as 1-2, 3-4 and 5-6
not sure about (13)-(14)…. It’s the same terminal.

As suggested above, the black wire in 7 showing too much copper at the moment, should be in A1
 
(13) and (14) normally denote auxiliary contacts often of a lower current carrying rating. Your contactor is deemed four pole so it is assumed they are the same rating as the others but are noted for auxiliary purposes also.
 

Reply to Contactor wiring help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
816
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock