Peter Woodford

Guys,

was wondering if you could help carried out a continuity test on R2 today on a ring circuit and was getting a open circuit. Tested R1 and got around 22 ohm connected R1 + R2 and got 46 ohm but the R2 is showing open circuit on its own. Have checked all sockets to see if there is a loose cable but nothing please help. Also did a RCD test on circuit and rcd tripped at 14.7 which is o.k so how is this going down to earth


Pete:mad:
 
Last edited by a moderator:
Hello and welcome Peter
How are you taking R2 tests ? wander lead and screw on socket ? could have drylining box or plastic lugs if so
Regards
Kung.
 
Guys,

was wondering if you could help carried out a continuity test on R2 today on a ring circuit and was getting a open circuit. Tested R1 and got around 22 ohm connected R1 + R2 and got 46 ohm but the R2 is showing open circuit on its own. Have checked all sockets to see if there is a loose cable but nothing please help. Also did a RCD test on circuit and rcd tripped at 14.7 which is o.k so how is this going down to earth


Pete:mad:
when you say R2 rest are you talking end to end ?
is it twin & earth or singles in conduit ?
 
Hey.

Have you checked your meter and leads on another circuit to make sure they're ok??

Sounds like a high resistance/open connection on the ring there somewhere, you havn't got a full loop but obviously there is an earth in the circuit because you have an R1+R2 reading albeit very high.
 
hi pete
to confirm ring cont L-L 22ohms do you mean .22
cpc-cpc open circ
what was n-n.
when you tested r1 and r2 did you do figure of 8 live out with cpc in and live in and cpc out then check all points on ring
 
when you say R2 rest are you talking end to end ?
is it twin & earth or singles in conduit ?

yes end to end on twin and earth

cheers

hi pete
to confirm ring cont L-L 22ohms do you mean .22
cpc-cpc open circ
what was n-n.
when you tested r1 and r2 did you do figure of 8 live out with cpc in and live in and cpc out then check all points on ring


n-n was the same as L-L any ideas
 
Last edited by a moderator:
Yes sounds like a break in cpc ! rcd test on each socket will still work down one leg.
 
Last edited by a moderator:
There must be a break somewhere but not necessarily behind a socket outlet.

As been said, best thing to do is split into 2 radials and follow it round till you find the part of the circuit that has the problem.

Not an easy task but reasonably easy to do.
 
Hey.

Have you checked your meter and leads on another circuit to make sure they're ok??

Sounds like a high resistance/open connection on the ring there somewhere, you havn't got a full loop but obviously there is an earth in the circuit because you have an R1+R2 reading albeit very high.


checked leads all O.K would this still pass on a cert


cheers
 
R1 + R2 prob high as you have a break in the cpc ! dont matter about rcd test it still works down either cpc leg find break and your get better R1 + R2 reading.
 
hi peter its funny no reading on R2 but( R1+R2) = 0.48
caculation for 30 meters 0.58 so not far off you have cpc,s loose in a socket
thatsw if you have checked your meter is functioning properly
 
R1 + R2 prob high as you have a break in the cpc ! dont matter about rcd test it still works down either cpc leg find break and your get better R1 + R2 reading.


If I can't find break can I still put on test result as I have just done Part P course and NICEIC are coming out to see the replacement of fuse board as my major job


cheers
 
Hi Peter
No he wont be happy with that as jason said best to split ring in middle and do IR test down both legs untill you find offending fault.
Regards
Kung.
 
If I can't find break can I still put on test result as I have just done Part P course and NICEIC are coming out to see the replacement of fuse board as my major job


cheers
peter you have a simple problem it will not take much to correct how will it look
if they come to assess you and ask you to do a ring continuity test for them
 

Reply to Continuity testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock