Discuss Continuity testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Or still split the ring into 2 20A radials, but that would mean that a number of sockets have no earth.
But at least this way you can R1/R2 back towards the cu.
Much easier to fault find on a radial.
As Kung said, the NIC man will not be best pleased if you leave as is.
Good luck and anymore questions, just ask.
agree with kung......... 1st have a look behind each socket if no joy.
take socket off half way round ring, split cpcs then do continuity on each half back to cu, one side should be ok and one open,keep splitting the bad half till you find the bad leg.
Reply to Continuity testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...