Fm-sam

Testing a lighting circuit with a long lead, all readings R1 R2 Rn around 0.6 to.08 ohms. Adding R1 + R2 = more than 1 ohm. Is this acceptable for recording as the result or should it be less than 1 ohm. TT system.
Thanks for any advice
 
Nothing wrong with the reading being in excess of 1ohm at all as long as it tallies up with the theoretical calculated length.

As a rough guide you could check your results against the published resistance values for various cable sizes in the OSG.

Bear in mind they wont be identical due to a number of factors but it should give you a rough idea.
 
Thanks for the quick reply. Had already checked cable length against OSG table ohms/m everything was fine so thanks. Only a novice so needed reasurance. Thanks again.
 

Reply to Continuity Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
996
OLDBOY
O
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
822
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
598
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock