1.25ohm external earth fault loop impedance on TN-S supply to building

Supply authority stated our only option is a TT conversion as they will not covert to PME.

What would be my best course of action when converting to a TT as the building is quite old and i do not want a 100ma main switch for diversity reasons and nuisance tripping, so Would it be suitable to convert to TT and have all final circuits in a RCBO with a board charge?
 
Page 33 OSG (yellow) has an example you're suggesting, i.e. for new A3 CU's.

Wylex have just released a SPswN RCBO, and use a bespoke gland for tail entry.
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass
 
Never installed or seen an earth mat, guess someone here has, or perhaps ask one of the manufacturers.

Out of curiosity, why won't your DNO convert to PME?
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass
A sweep with a cat, not the feline kind, should help you avoid any other services.

SDS adapter and you can have a rod in the ground in a few seconds with little effort.
 
One question, will the rod be a better bet than the poor TNS earth?
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass

We install mats regularly.

You will still need to dig down about 300mm but you will be able to CAT scan the area accurately.

The reason mats are deemed safer is that most Permit to Digs instruct you to CAT scan every 300mm. You cannot do this when driving an earth rod in.
 

Reply to Converting to a TT system... possibly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
554
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock