Discuss Cooker circuit in the UK Electrical Forum area at ElectriciansForums.net
Rappid
Changing a CU plus many other jobs for a customer.
Testing the circuits before the CU change and found the oven connected to the cooker circuit in a JB behind a base unit, the JB screwed to the wall and only accessible by removing the base unit as there is no access from inside the base unit, there is no cooker switch to provide isolation. I only found it by sticking my inspection camera up behind the base unit
Do I put NV on the certificate or do I have to start ripping the units apart to get the junction box?
I know the customer won't pay to get a switch put in as they have cancelled some of the work due to lack of money.
Don't start the bloody cooker isolation switch debate again! :) Daz
No local isolation though. Oh Christ, the debate is going again and I'm getting drawn in. Help !!!!! Daz
Well, can't you pull the cooker out and do a Zs on the cooker connections?
Will have a look tomorrow and see if the connections are accessible, don't really like taking working appliances apart cos if something goes wrong wether we touched it or not, we are always to blame.
Pleaase.
Local isolation is NOT mandatory. If the circuit breaker is accessible,and can be locked off, then that can be the isolator.
It is always useful to have local isolation, but not necessary in most/many domestic situations.
Usual caveats apply - manufacturers installation instructions.
The JB behind a kitchen unit does not comply as it cannot be accessed. That'd be a C3 in my view on a EICR.
whats the A rating of OPD on the cooker circuit?
that joint box may be 30A...there again it may be a 20A so....
use the wander lead to verify R2 is present and continuous....R2 is between furthest points so you should get a positive at a screwhead on the cooker....
if it aint there....fail it....
Reply to Cooker circuit in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...