Discuss Cooker circuits fusing down ??? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Wilson12
Trainee
Hello
I’ve pulled out a electric oven and the connection plate at the back for the cooker circuit has 2.5mm hardwired to the 6mm circuit for a 1.76kw load and also a 6mm connecting a induction hob,unknown load.
Does the 2.5mm need to be fused down or is it okay being spurred off the cooker circuit?
Hi - sorry to start with this - what do the manufacturer’s installation instructions have to say?
I assume it’s got a 32A mcb on the circuit?
The 2.5 doesn't necessarily need fusing down as the oven is likely to be a fixed load which is not subject to overload. In this case cables can usually be sized according to design current rather than nominal current.
Hi - if manufacturer is silent and the 2.5 mm flex is suitable I’d press on. The circuit 6mm twin and earth has 2.5mm cpc which is deemed fit for purpose. The 2.5mm flex has the same size conductor for cpc so I don’t see an increased risk during fault clearance :) .
Reply to Cooker circuits fusing down ??? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...