Hello
I’ve pulled out a electric oven and the connection plate at the back for the cooker circuit has 2.5mm hardwired to the 6mm circuit for a 1.76kw load and also a 6mm connecting a induction hob,unknown load.
Does the 2.5mm need to be fused down or is it okay being spurred off the cooker circuit?
 
Aico 3000
Wilko

Wilko

-
Esteemed
Arms
Hi - sorry to start with this - what do the manufacturer’s installation instructions have to say?
I assume it’s got a 32A mcb on the circuit?
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
The 2.5 doesn't necessarily need fusing down as the oven is likely to be a fixed load which is not subject to overload. In this case cables can usually be sized according to design current rather than nominal current.
 
Barnaby Stedman

Barnaby Stedman

-
It is safer to fuse down 2.5mm if it was on a 6mm cable - in case some dumbo comes along and adds a socket to a 'ring final circuit' and then something overloads etc.
but that's only a precaution
 
B

Bobster

It is safer to fuse down 2.5mm if it was on a 6mm cable - in case some dumbo comes along and adds a socket to a 'ring final circuit' and then something overloads etc.
but that's only a precaution
If every circuit was designed for "what ifs", the costs involved would be horrendous.
 
D

Dustydazzler

-
Esteemed
Arms
2.5 on a 32a mcb

Hardly the worst electro crime in the world
 
Wilko

Wilko

-
Esteemed
Arms
Hi - if manufacturer is silent and the 2.5 mm flex is suitable I’d press on. The circuit 6mm twin and earth has 2.5mm cpc which is deemed fit for purpose. The 2.5mm flex has the same size conductor for cpc so I don’t see an increased risk during fault clearance :) .
 
alban moffitt

alban moffitt

-
how many other appliances are on this 'cooker circuit' as you have mentioned this oven and also a hob.
 
Get paid faster with card payments | Go Paper Free - Save Hours | Offer Finance to Customers
This official sponsor may provide discounts for members

Reply to Cooker circuits fusing down ??? in the Electrical Courses and Electrical NVQ's area at ElectriciansForums.net

CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Top Bottom