Hi all,

I have just been to a job where the existing hob is wired in using 2.5mm heat resistant cable, the hob is rated at 6000w. I calculate this to need a 4mm cable, however, was challenged by someone, in the end I called NICEIC who stayed neutral and said it "might be ok, what do the instructions say" instructions dont specify the cable size needed.

What size cable would you guys use?

Many thanks in advance,

M
 
6000/230=26A

Diversity: read Appendix A in your OSG, and the allowance for cookers is in table A1. This will give you your design current for the circuit. Come back to us with that.

Hang on, there's an oven on it as well?
 
6000/230=26A

Diversity: read Appendix A in your OSG, and the allowance for cookers is in table A1. This will give you your design current for the circuit. Come back to us with that.

Hang on, there's an oven on it as well?
Yes there is a 13 amp oven. I understand the diversity part e.g. first 10 amp plus 30% of the remainder, however, the circuit is pre existing, I am referring to the cable literally the connection point to the hob.
 
Yes there is a 13 amp oven. I understand the diversity part e.g. first 10 amp plus 30% of the remainder, however, the circuit is pre existing, I am referring to the cable literally the connection point to the hob.
Oh and there is a socket so rated current is
What do the manufacturers instructions say?
They dont, they just specify the heat resistant cable and not the actual size, I called them (Zanussi) and they said they didnt know and to email in.
 
Ah I see. I presume ref method C?

From about P400 of the BS7671 you'll find the tables for current carrying capacity for various cables. Yours would be 2.5mm, multicore, presumably 90deg if it's heat resistant, and it's not armoured. Have a butchers and tell us the CCC for your cable
 
Ah I see. I presume ref method C?

From about P400 of the BS7671 you'll find the tables for current carrying capacity for various cables. Yours would be 2.5mm, multicore, presumably 90deg if it's heat resistant, and it's not armoured. Have a butchers and tell us the CCC for your cable
26 amp when in free air. I guess that answers the question, but is very close to the mark.
 

Reply to Cooker connection unit to hob cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
853
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
643
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
573
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
677
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
584

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock