10.8 KW combinedDo you know the combined kw of both appliances.
Discuss Cooker installation advice in the UK Electrical Forum area at ElectriciansForums.net
10.8 KW combinedDo you know the combined kw of both appliances.
As said dual outlet. Click do a gooden.Noted, it’s just about where both appliances are terminated , can u feed them both to one cooker switch.
No problem. One cable to the dual outlet and connect both appliances to it with diversity applied they will rarely achieve that for a sustained period.10.8 KW combined
On this occasion, 32A + 16A =48A
The other options are probably not available.
What did the electrician that came out say?
After all they have the best information and knowledge of the installation.
applying diversity to 48A. ( 10A+ (38A x 0.3)) = 21.4A. add 5A if isolator has a built in socket.On every occasion 32 + 16 =48,thats a simple mathematical truth.
However that is not the correct way to calculate th eload on this circuit, you need to apply diversity.
Reply to Cooker installation advice in the UK Electrical Forum area at ElectriciansForums.net