Hi there - just been out to install a cooker. After confiming that the circuit is OK next was testing the cooker.
It is a 2nd hand cooker that the owner bought for £50. Checked earth continuity and that was fine. Moved onto the IR tests. Oven was OK with 33.8M ohms. Then the rings. This is were I need a bit of guidance.
1 ring gave me a reading of around 4M ohms, so that is fine. The other 3 gave next to no resistance at all, around 0.1M and less.
So not too sure if the rings are OK as I know you can get very low readings. Just strange that one is OK.
So I have done a functional test. Oven OK and 3 of the rings work but 1 trips the RCD, so suspecting that the element has failed.
But still concerned that 3 of the rings failed the IR test.
Have told the user that I'm not connecting the cooker.
Any advice please guys.
Cheers Rich
Cheers Rich