Alison

New kitchen fitted. Company's electrician came to connect cooker on Friday afternoon. Told me when he left all ok to use. Sunday, went to cook Sunday lunch. Trip in fusebox keeps going.

Looked under new kitchen unit to find cover that goes over wires on back of cooker the on floor. So decided to pull out cooker and found what is in the photos here.

What do I say or do when they come back on Monday ?




Picture 337.jpgPicture 339.jpg
 
Hi Alison, that is not the work of an Electrician.
 
What do I say or do when they come back on Monday ?
/QUOTE]
A Has this circuit been tested?
B Why was it not installed on a proper cooker outlet?
C Why has the stranded CPC not been sleeved?
D Why is the cooker tripping the RCD?
E Are you aware that leaving the terminations like this could have caused a shock risk?
F Are you properly qualified and experienced?
G Does your manager/supervisor know you carry out work to this standard?
H Can I have his/her phone number?
I Do you have something else to do because you're not touching this until your manager/supervisor has seen it and commented?
 
New kitchen fitted. Company's electrician came to connect cooker on Friday afternoon. Told me when he left all ok to use. Sunday, went to cook Sunday lunch. Trip in fusebox keeps going.

Looked under new kitchen unit to find cover that goes over wires on back of cooker the on floor. So decided to pull out cooker and found what is in the photos here.

What do I say or do when they come back on Monday ?




View attachment 25305View attachment 25306
Hi Alison.

Get those little sh**s back round there to sort out this crap.

Thanks Love.
 
Their replies are better than mine, go with whichever suits at the time.
 
It is rough, but it may not be the wiring causing the tripping. I've had 2 brand new ovens in the last year that tripped the RCD.
Moisture in the element I think. If warmed up properly on a non-rcd circuit, they are usually ok when put back on the RCD.
 
If this work is the standard of the company's I would be getting everything that they torched electrical looked at & tested IMO !
 
and ask him if he knows what a ring crimp is. it's not something to stop him farting.
 
Another prat P cock up I would imagine, get them back with a proper sparks this time, cowboy job of the highest order.
 
I would refuse to have them back in the house. I would recommend you phone the company fitting your kitchen and ask for a supervisor to attend your home. When he comes around to see you show him the shambles you have identified and ask him if he can send a Professional electrician around to carry out any electrical works becaise you are concerned for the safety of your family. If he refuses I would recommend you phone trading standards immediately and e-mail them the photos you have shown us and they will or should take action.
 
I would refuse to have them back in the house. I would recommend you phone the company fitting your kitchen and ask for a supervisor to attend your home. When he comes around to see you show him the shambles you have identified and ask him if he can send a Professional electrician around to carry out any electrical works becaise you are concerned for the safety of your family. If he refuses I would recommend you phone trading standards immediately and e-mail them the photos you have shown us and they will or should take action.
yes Mike....

but they have 3 opportunities to correct their work....

the guy on the elecsa stand was quite clear about that one when i handed over those images of the chud found by UKsparks......

quite clear about it....i left him quite clear about what i thought as well.......
 
First thing that went through my mind? The OP wanted a cheap job done and now isn’t happy with the results.

Call me cynical if you like but I’ve seen a few jobs like this and the customer had wanted a cut price job each time.
A reputable company will do a good job and provide the service to match. Unfortunately it costs.
 
To be fair Tony, I've seen lots of stupidly expensive jobs that have been bodged to this standard
 

Reply to Cooker trips breaker in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
710
We have one room that seems to have lost most of its power last night. One of the outlets in the rooms has a power strip plugged in that powers...
Replies
5
Views
769
Even if the cooker and the plug is turned off it still trips after about an hour. It doesn't immediately trip out but it usually always turns back...
Replies
1
Views
824
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
263
Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
643

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock