Hmm, I didn't get a reply notification; anyway
How could a neutral be anything but dead when it's grounded at the panel?
Open a neutral under load, and it will float up to 120 volts.
Discuss Correct grounding of metal junction box w/splices for 3 circuits in the USA area at ElectriciansForums.net
Hmm, I didn't get a reply notification; anyway
How could a neutral be anything but dead when it's grounded at the panel?
Open a neutral under load, and it will float up to 120 volts.
Yes, normally that would happen on the load side of the break.
However the proposed situation of joining three neutrals together would prevent the voltage rise from occurring, but it would overload the other two neutrals.