Discuss Correct Procedure??? in the Industrial Electricians' Talk area at ElectriciansForums.net
E
essexboy
Thanks for taking time to read this thread
having obtained my 2381 ,2330 i`am now in the process of getting a notifyable job done for my niceic assessment unit but need some advice on the correct and legal way to go about it.
my consumer unit needs upgrading so this makes it the ideal job to keep niceic hopefully happy and for me to get a pass.
i have a 60amp service fuse ,16mm conductors (P+N) into the meter and 16mm tails up to the old 60amp/rcd consumer unit and a 6mm main earth from incomer to the MET (tn-s)
i would like to install a new 100Amp/80Amp30Ma rcd split load consumer unit and upgrade tails to 25mm2
i have notified building control and awaiting there reply ,and need to now the correct order to complete the work??
should i wait for BCO reply
arrange for DNO to upgrade service fuse, P+N+E conductors and install isolator
before i install the new consumer unit???
or wait for BCO reply
arrange for DNO to fit isolator
then arrange for DNO to come back to upgrade conductors???
i would be most grateful for any help as i want to get this right :)
as long as you have given building control two working days notice, you can commence with the work, you are only notifying them you are doing it - not asking their permission
just speak to the DNO and see which way they want to play it
once the supply is isolated, do your CU change (including tails) and they can do their work in one go
Reply to Correct Procedure??? in the Industrial Electricians' Talk area at ElectriciansForums.net
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...