Reaction score
55
Had a really weird one this week.
Customer complaining about getting shocks from a power shower.

Inital investigations showed reaction from my volt stick from the shower hose! (All be it not full mains)

Took the lid off and the plumber who recently installed the shower had connected the neutral and earth the wrong way around!

Odd thing was that the power shower still worked..? Checked the fused spur in loft where power shower was fed from and seemed to be connected correctly (all be it very untidy). Not certain which circuit it was fed from but there was limited RCD protection for the house. (sockets only)

My question is:: Why didn't anything trip out!? how did the shower function with the CPC as the return path? Only thing I can think is that it using the common connection at the PME terminal but still doesn’t explain why it didn't trip the MCB at least... what do you guys think?
 
If you consider the MCB, it's only monitoring current In the live feed. It won't know the current is returning via (E) rather than (N)!
But an RCD should see the difference. Perhaps there wasn't one in this circuit?
Not odd the shower worked considering (N) and (E) are connected together somewhere - a good job they are!
 
If you consider the MCB, it's only monitoring current In the live feed. It won't know the current is returning via (E) rather than (N)!
But an RCD should see the difference. Perhaps there wasn't one in this circuit?
Not odd the shower worked considering (N) and (E) are connected together somewhere - a good job they are!
There is either no rcd on the circuit or its a malfunctioning rcd. The mcb did,nt trip because it was, nt being overloaded. The shower is, nt faulty. Its likely a TNC-S system so the earth wire is in effect acting like an alternative neutral
 

Reply to CPC as a functioning return path!!!??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
553
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
831
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock