Discuss cpc in pvc conduit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
15
Hi all, I was testing an installation today and every thing seems to be in order till I found a piece of white pvc conduit with a single 2.5 brown cable in it with no cpc. The conduit had been installed to pick up a permanent feed to a PIR from an emergency light fitting.
Both lights and the PIR were all earth correctly Just not through this conduit link. Now my question is, is this allowed? If I was running the cable I would put a cpc in there as as it forms part of the circuit it should have a cpc. Is there a reg relating to running a cable this way. Of course if the conduit got damaged there would be no earth path via the conduit, so the cpc may pick up the fault but there is no guarantee that the cpc and the live conductor would be damaged at the same time???
 
Hi all, I was testing an installation today and every thing seems to be in order till I found a piece of white pvc conduit with a single 2.5 brown cable in it with no cpc. The conduit had been installed to pick up a permanent feed to a PIR from an emergency light fitting.
Both lights and the PIR were all earth correctly Just not through this conduit link. Now my question is, is this allowed? If I was running the cable I would put a cpc in there as as it forms part of the circuit it should have a cpc. Is there a reg relating to running a cable this way. Of course if the conduit got damaged there would be no earth path via the conduit, so the cpc may pick up the fault but there is no guarantee that the cpc and the live conductor would be damaged at the same time???
I would say definately no, having a live phase conductor in a pipe without an earth with it not right, if a metal pipe which was earthed then not so bad, however I don't like the fact a single core run alone anyhow, I have no BGB with me but there is no doubt a reg will exist somewhere regarding an earth at all points and conductors running alone in non earthed containment, someone with a regs may help out, but your concern is valid IMHO.
 
not sure if what you have stated is correct? circuit protective conductor, protects the circuit, not the same as bonding or earthing?
Bonding is connecting extraneous conductive parts to earth...

Defination if a cpc taken from BS7671: A protective conductor connecting exposed conductive parts of equipment to the main earthing terminal.

This is the same defination as earthing so yes earthing and cpc are the same.

Don't let the name confuse you squire, it isn't there to provide an earth path if the cable is cut or even protect the circuits length at all.
 
Won't the conductor get lonely without a neutral and CPC ;)
Apart from loneliness I wouldn't see a good electrical reason that it wouldn't be acceptable as described in this particular scenario. Is there actually a reg in the 7671 that prohibits it?
 
What sort of test are you carrying out? IV or EICR?

The nearest thing to it is reg 543.6.1 but that doesn't require the cpc to be run adjacent to every conductor of the circuit so I don't think you can actually justify 'failing' this
 
Last edited:
What sort of test are you carrying out? IV or EICR?

The nearest thing to it is reg 543.6.1 but that doesn't require the cpc to be run adjacent to every conductor of the circuit so I don't think you can actually justify 'failing' this

(EICR)
It more than meets the requirements of basic protection but I not sure if it would meets the requirements for ADS?
It's a tricky one and as we all know the regs can be full of contradictions.
 
Well it is a tough call, in the old days a double insulated single core was the norm in houses run between switches etc, regs change all the time though and I cannot actually quote a reg (if there is one) to suggest a fail on the EICR, bad practice I would suggest but again no reg no fail, we need someone with a regs book to look closely at section 4.
 
A length of conduit is not a point. You have already stated that there is a cpc at all points in the wiring, so what is the problem?
 
Well you could argue if the conduit was damaged the phase conductor inside could become damaged and a potential electric shock for someone, the supply would not switch off if no other core run alonside it, thats one argument.
 
Well you could argue if the conduit was damaged the phase conductor inside could become damaged and a potential electric shock for someone, the supply would not switch off if no other core run alonside it, thats one argument.

That doesn't mean that there is a requirement, however. In fact even with a cpc run alongside the phase conductor there is absolutely no certainty that the phase wouldn't be damaged without creating an earth fault.
 
If it is an EICR then it cannot 'fail' it can merely be found unsatisfactory and a suitable code given.

Is it immediately dangerous?
Is it potentially dangerous?
Does it require improvement?
 
If it is an EICR then it cannot 'fail' it can merely be found unsatisfactory and a suitable code given.

Is it immediately dangerous?
Is it potentially dangerous?
Does it require improvement?

I can't see any breach of the Wiring Regulations unless it was to enter a ferrous enclosure on its own at some point.
 

Reply to cpc in pvc conduit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
308
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
387
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock