Marcus Vaughan

-
Esteemed
Reaction score
240
Crabtree RCCB not tripping -help! upload_2019-2-18_9-6-34 - EletriciansForums.net

Hi all.

So the Crabtree old style in my hand failed the I delta n test (times 1). But passed the 5 times test.

So I have replaced it with the one in the board. Supposedly reconditioned - and that’s failing both tests but mechanical works.

I am wondering if I am missing something here with my testing.

I am testing through a socket outlet.

Anyone any ideas other than replace with new?
 
Have you checked for N-E faults? These can interfere with both MFT tests and the operation of the test button.
 
Have you checked for N-E faults? These can interfere with both MFT tests and the operation of the test button.

I’ve not tested all those protected circuits no. Just the one I have been working on.

I think I’ll swap out with another RCCB before tackling that one - off to pick one up now.
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
 
Thanks Wilco.

I certainly considered not swapping out the original - seeing as it passed the 5 times test - as as you say - is only for additional protection.

I’ve just swapped it out again - and it’s now working.

But - when I tested at the socket outlet - no joy - but tested at the board (to be honest) - and it’s fine.

I’d like to get my head round what’s gone on here.

Best get back to work.....
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
That handbook is out of date now.
 

Reply to Crabtree RCCB not tripping -help! in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock