Hello all,
I've got an unusual fault on a cu main switch in a Wylex split load board. I was called to a property with no power. The main switch was in the off position and both rcds and all breakers were in the on position. There was a leak on the toilet but no water through the electrics. Checked it over and switched the main switch back on.
I was upstairs with the plumber when 5 minutes later power goes off and main switch had dropped again. Switched back on, went back next day, checked property, changed main switch for new one, polarity correct, Ze 0.28, PFC 0.83, ins res >299 on all circuits except down sockets which was 154. Ramp test 27 Rcd test 28/13 on both rcds.
Question was asked if anyone had switched main switch off which didn't go down very well. Property was solar panels. Never come across this before, any guidance would be most helpful.
I've got an unusual fault on a cu main switch in a Wylex split load board. I was called to a property with no power. The main switch was in the off position and both rcds and all breakers were in the on position. There was a leak on the toilet but no water through the electrics. Checked it over and switched the main switch back on.
I was upstairs with the plumber when 5 minutes later power goes off and main switch had dropped again. Switched back on, went back next day, checked property, changed main switch for new one, polarity correct, Ze 0.28, PFC 0.83, ins res >299 on all circuits except down sockets which was 154. Ramp test 27 Rcd test 28/13 on both rcds.