You will need to do all the useuall test on each circuit:

Continuity of protective conductors including main and supplementry bonding
Continuity of ring final circuits
Insulation resistance
Polarity
Earth loop impedence (Zs)
External impedance (Ze)
PFC


You might want to do this before you change the cu incase there is a problem with one or more of the cicuits. GN3 is a great book on the inspection & test procedure.

And you will have to notify local building control because it falls under part p.

hope this helps:)
 
Not as of yet, but as long as i issue a cert and notify building control i am ok, this is what i believe anyway??

You are right but you have to notify building control before you start the work so they can come out and see it during the work and then after and they will do an Inspection & test. This will also cost you but not sure how much. Where I live its about £110 for jobs under £2000. But in a near by city its about £500, so it depends how much your lbc will charge.:confused:
 
You are right but you have to notify building control before you start the work so they can come out and see it during the work and then after and they will do an Inspection & test. This will also cost you but not sure how much. Where I live its about £110 for jobs under £2000. But in a near by city its about £500, so it depends how much your lbc will charge.:confused:
quite right about notifying before work starts but i wouldnt think they would check a cu change beforehand as its all exposed

dont forget earthing and bonding before you start the work
 
Ok thanks for all the info, so if bonding is not there is it a must that it is done before the work or do i note it down on the cert and then the customer decides whether to have it done?? Also what is the best way to test the bonding or anything else that is far away from the cu, will i need an extension reel for my tester??
 
Agree Check bonding and tails etc also before a cu change i always do continuity and ir tests ! you may open up a can of worms and if you do your prepared for it !
 
Agree Check bonding and tails etc also before a cu change i always do continuity and ir tests ! you may open up a can of worms and if you do your prepared for it !
oops :eek: forgot to mention tails, cant believe someone who has already changed cu`s is asking these questions :eek:
 
i would advise some additional training before attempting the work, its a bigger job than people think and can cause a lot of problems, judging by your questions i would doubt your competance.
Gn3 will give you a lot of info on the testing procedures also look up on earthing and bonding
 
As above test first before you dis the existing. Is this for your assessment ? I thought you had to be registered To become a arms member?
 
so if bonding is not there is it a must that it is done before the work or do i note it down on the cert and then the customer decides whether to have it done??

customer :eek: if the bonding isnt there or isnt up to scratch dont do the job if customer wont agree ! you will need a wander lead for bonding testing if you dont have one make one ! If its for an assessment most people do their own CU change or rewire or for a mate or family etc as its easier to get them to agree on what needs doing ! if its for an assessment make sure your install is up to bs7671 as you will fail if it isnt and if not for assessment then the lbc will tell you what you need to do to rectify it before they test/insp and issue your cert.
 
Last edited by a moderator:

Reply to CU Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening all, Just a quick question, I am an electrical maintenance engineer and have 18th edition, inspection and testing and so on, so I get...
Replies
17
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
809
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
1K
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
215

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock