Hi everyone
ive got my AM2 coming up and im unsure about the over load settings for the D.O.L, ive seen 2 different equations and im trying to work out which is right.
so say my motor is 750w would my calculation be 750/400/1.732/0.8 = 1.35
or
750/400 x 1.732 x 0.8 = 2.59
i bought a course to learn and they use the second equation and some how got the first equations answer?
thanks in advance.
 
i.e if the rating plate says 10A you set the overload at 10A. although it used to be common practice to set at 10% over FLC.
 
i.e if the rating plate says 10A you set the overload at 10A. although it used to be common practice to set at 10% over FLC.
ok have you done the AM2 in the uk? just both my tutor and training video said this is the formula.
only problem is i cant remember whether he said to divide or times for the formula and the training video has both.
but if you have done the AM2 in the uk then your answer could be right.
 
i.e if the rating plate says 10A you set the overload at 10A. although it used to be common practice to set at 10% over FLC.
In the AM2 you only get the output power so what would the equation be to determine the FLC, would it be I= P/Vx1.73x0.8 also where does the 0.8 value come from

ive also attached basically what you get in the AM2 bay this is from a training rig at college
 

Attachments

  • E+eLCBnwSQmM101OdDPUwQ.jpg
    466.4 KB · Views: 65
Another question about the DOL. when testing IR. should I disconnect cables from the contactor? Or will it be able to take the 500v
 
Last edited by a moderator:
would my calculation be 750/400/1.732/0.8 = 1.35
or
750/400 x 1.732 x 0.8 = 2.59

Think about what each term means and you will see that the second version has a simple mistake: it has been written with the brackets missing that show the order of calculation. If you put the brackets in, the two formulas are the same and give the same result.

The aim here is to calculate the line current from the the power P, by dividing it by the line voltage V (line), also dividing it by sqrt (3), and also dividing it by the efficiency / power factor term (0.8).

I (line) = P / V (line) / sqrt(3) / 0.8
= 750 / 400 / 1.732 / 0.8
= 1.35A

Logically the second version must be wrong because it's implying three phases carry less power than one phase per line amp and that the motor has an impossible over-unity power factor. But re-write it with the brackets and all is good:

750 / (400 * 1.732 * 0.8)

Multiply what is inside the brackets first, then divide the power by that intermediate result, and you have the correct answer of 1.35A again.

would it be I= P/Vx1.73x0.8

And you're being careless with brackets too!
 
In response to tel, you're showing your age, we don't recommend setting any overload beyond the rated capacity of the motor, if the motor is running continuously at just over full load then you can get a runaway effect and overheat the motor without the overload operating in time, your advice relies on a comfort margin and a short lived overcurrent which means the overload won't trip as designed on some cases, might be rare but it still is a factor of motor failure.
 

Reply to D.O.L starter overload settings in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi everyone, I’m doing my am2 and can’t seem to find a definite calculation to working out the overload this equation I = P/V/1.73/0.8 has popped...
Replies
0
Views
2K
asking advice: I had the AM2 assessment today and there’s a couple of things I wanted to check with someone that may have done this recently. the...
Replies
0
Views
2K
Hi I’m sitting my AM2 next month and have found out that you need to set an overload on a direct online starter motor circuit. I have tried...
Replies
9
Views
10K
Hi Everyone, I'm hoping someone might be able to help answer a question which i have long pondered over. Firstly i am not an electrician, please...
Replies
9
Views
12K
M
Hi has anyone recently done the am2? I just wanted a basic calculation for setting the overload (they give you motor rating in Kw) for the 3...
Replies
40
Views
19K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock