Discuss Damp problems in sockets... solutions? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,600
I have a customer who lives in a grand old house which suffers from damp.

The ground floor sockets (2 different circuits) IR test at around 0.3Mohms L/N-E. This was actually 0.01Mohms but I have already done some fault finding and managed to improve it.

Most of the back boxes are very rusted and flaking to bits with moisture inside them. As stated, I have done some improvements to the sockets and boxes but this has only managed to get the IR up to 0.3Mohms (L/N-E). I have looked thoroughly for any more sockets/FCU's that I may have missed but I now feel the remaining fault(s) are within the walls, even though this doesn't make sense as I can't see how moisture would have got inside the cable (Its black/red metric PVC).

I think the existing cables have metal capping within the damp walls, but again, even if this capping is rusting I cant see how it will affect the PVC covered cable. The wiring is approx 25 years old

My questions are..

1. What can you do about damp? It's pointless to rewire as the damp problem will still be there. Are there ways to protect the boxes and sockets from damp?

2. What are the solutions if I cannot raise the IR above 0.3Mohms? I'm guessing I have to map out the entire circuit, and find every single fault, but then what? It's an immaculate house, surface trunking not an option, new cable in wall not really an option as existing damp problem already somehow affecting cables in walls (unless some kind of cable joints in walls which are affected).

3. Are these designed to be installed in the wall? 2 Gang 35mm PVC Flush Box Round Corners with 20mm Conduit KO White (Sold in 1's) - https://www.cef.co.uk/catalogue/products/1063228-2-gang-35mm-pvc-flush-pattress-box-round-corners-with-20mm-conduit-ko-white

Usually fault finding is easy. 1 fault, bit of IR testing, fix fault. In this case there are faults everywhere and not just in the actual sockets!
 
Last edited:
Sounds like significant damp if it is rusting things noticeably. I guess they really should look at getting it treated.

Regarding the circuit, id be tempted to map it out completely, disconnect all sockets/FCu's and everything so you just have the cable ends sticking out of the wall..........then do your continuity and IR tests on each leg noting the results. From this you can build up a better idea of the faults that exist............who knows, it may only be 1 troublesome leg where you might be able to re-route that leg in a bit of D-line on the surface or something that avoids damaging the decor.

I think you really need to find the issues on the circuit first off. Also dont discount something random somewhere giving odd results........seen plenty of outside lights spurred straight from the back of a socket that were giving issue's.
 
I can't imagine any flush mounted accessories would be possible without sorting the damp issue first. Sounds a nightmare.
 
Rising damp is usually treated by injecting a chemical DPC into the wall, and then rendering to a height of 1m up the wall with a damp resisting render. Belt and braces.

However I have found when cutting into such walls, that they can still be damp behind the render, so perhaps the chemical DPCs aren't all they're cracked up to be. The render traps the moisture in the wall, resulting in permanently damp brickwork, whereas it might have dried out somewhat had it not been there.

So getting the place damp proofed may not be the silver bullet.

If I were to rewire a job like this, and the client wanted everything chased in, I would use plastic backboxes such as the one you linked to above (it says flush mount so I assume fine for this), and plastic conduit glanded in. Where bedding in any backboxes etc, I would use a strong 3:1 sand to cement mix, with a generous splash of waterproofing admix such as this (I have used this mix to patch repair damp-proof render such as above, and it works well):

 
I think getting the customer to call in a damp specialist is best advice. I did this once and they injected a DPC. It was an entire redecoration job but seems to have worked.

Only other thought is doing something unusual and extreme like running conduit outside and through to surface mounted accessories
 
I have a customer who lives in a grand old house which suffers from damp.

The ground floor sockets (2 different circuits) IR test at around 0.3Mohms L/N-E. This was actually 0.01Mohms but I have already done some fault finding and managed to improve it.

Most of the back boxes are very rusted and flaking to bits with moisture inside them. As stated, I have done some improvements to the sockets and boxes but this has only managed to get the IR up to 0.3Mohms (L/N-E). I have looked thoroughly for any more sockets/FCU's that I may have missed but I now feel the remaining fault(s) are within the walls, even though this doesn't make sense as I can't see how moisture would have got inside the cable (Its black/red metric PVC).

I think the existing cables have metal capping within the damp walls, but again, even if this capping is rusting I cant see how it will affect the PVC covered cable. The wiring is approx 25 years old

My questions are..

1. What can you do about damp? It's pointless to rewire as the damp problem will still be there. Are there ways to protect the boxes and sockets from damp?

2. What are the solutions if I cannot raise the IR above 0.3Mohms? I'm guessing I have to map out the entire circuit, and find every single fault, but then what? It's an immaculate house, surface trunking not an option, new cable in wall not really an option as existing damp problem already somehow affecting cables in walls (unless some kind of cable joints in walls which are affected).

3. Are these designed to be installed in the wall? 2 Gang 35mm PVC Flush Box Round Corners with 20mm Conduit KO White (Sold in 1's) - https://www.cef.co.uk/catalogue/products/1063228-2-gang-35mm-pvc-flush-pattress-box-round-corners-with-20mm-conduit-ko-white

Usually fault finding is easy. 1 fault, bit of IR testing, fix fault. In this case there are faults everywhere and not just in the actual sockets!
PVO??
 
External walls in old houses suffer this quite a lot, also chimney breast walls can be damp, rusting back boxes. I would advise getting a builder round to address the damp and treat, then replace all the rusting boxes and sockets if need be, this will help improve the IR big time.
Maybe minimize sockets on external walls if practically possible.
 
What's the outside ground level, is it flush, below or higher than the internal ground floor?

And if the area is below ground level then is it prone to flooding/high water table


This chap is good at explaining brick/water absorption

 
Last edited:
ventilationis necessary in old houses. might also help investing in a de-humidifier.
They have dehumidifiers in most rooms already. I think (like most have said), the only option is to spend a bit of cash and get the damp proof guys in.
 
I've had a couple of places injected with chemical dpc... it worked very well, but you have to make sure that the person doing it actually cares about what they're doing... and does it properly.

I've also used some stuff called Zypex (I think) years ago... it looks like cement and you just mix with water to create a slurry which is then painted onto the wall... so handy behind backboxes after you've chased them out.

You have to be careful with really old places with lime mortar / render... as they are supposed to 'breathe' and using any sort of damp proofing will just cause more trouble !
 
OK gentlemen and ladys just sold a house and this that I did having a bad damp.
1) chip all the plaster off 1mtr high
Spray walls with salt remover
2) inject a damp proof between the bricks two course high
3) slurry the walls with sbr
4) mix render with sbr
5 top coat with finish plaster
6) wait till 6 months paint walls after.
 
OK gentlemen and ladys just sold a house and this that I did having a bad damp.
1) chip all the plaster off 1mtr high
Spray walls with salt remover
2) inject a damp proof between the bricks two course high
3) slurry the walls with sbr
4) mix render with sbr
5 top coat with finish plaster
6) wait till 6 months paint walls after.
that's good. should just about last till the buyer's cheque clears. 🤣🤣🤣
 
Friend of mine has house which he has owned for years. Lived in it initially then rented it out after that. Old terrace with solid walls and concrete floor. I've lost count of what he's spent on damp proof injection, cement rendering, removing floor and laying damp proof membrane etc. Mostly done by professional people. House still has damp issues now.
 
Most of the damp is tracking a cross from one wall to the other, where debris betwen the bricks. And need clearing out
And a problem on a bay window taken the render off in side and hoover all the crap out, I bet one on here will say why did I not remove the bricks out side, answer accie bricks.
 
Were you testing from the board with all fixtures in place? If so I would split the legs and check if a particular one is dragging it down. In that situation i would immediately think the issue is not the wiring but the sockets. Is your reading of 0.3mohm with sockets ?
 
I have a customer who lives in a grand old house which suffers from damp.

The ground floor sockets (2 different circuits) IR test at around 0.3Mohms L/N-E. This was actually 0.01Mohms but I have already done some fault finding and managed to improve it.

Most of the back boxes are very rusted and flaking to bits with moisture inside them. As stated, I have done some improvements to the sockets and boxes but this has only managed to get the IR up to 0.3Mohms (L/N-E). I have looked thoroughly for any more sockets/FCU's that I may have missed but I now feel the remaining fault(s) are within the walls, even though this doesn't make sense as I can't see how moisture would have got inside the cable (Its black/red metric PVC).

I think the existing cables have metal capping within the damp walls, but again, even if this capping is rusting I cant see how it will affect the PVC covered cable. The wiring is approx 25 years old

My questions are..

1. What can you do about damp? It's pointless to rewire as the damp problem will still be there. Are there ways to protect the boxes and sockets from damp?

2. What are the solutions if I cannot raise the IR above 0.3Mohms? I'm guessing I have to map out the entire circuit, and find every single fault, but then what? It's an immaculate house, surface trunking not an option, new cable in wall not really an option as existing damp problem already somehow affecting cables in walls (unless some kind of cable joints in walls which are affected).

3. Are these designed to be installed in the wall? 2 Gang 35mm PVC Flush Box Round Corners with 20mm Conduit KO White (Sold in 1's) - https://www.cef.co.uk/catalogue/products/1063228-2-gang-35mm-pvc-flush-pattress-box-round-corners-with-20mm-conduit-ko-white

Usually fault finding is easy. 1 fault, bit of IR testing, fix fault. In this case there are faults everywhere and not just in the actual sockets!
Hello HippyHappyDad. This will be a tough one to find. The cables themselves will not be the problem - they work ok in damp environments. As above, remove every fitting you can find, dry the cable ends and test individually. My suspicion would be buried choc bar connectors plastered directly into a damp wall and hidden from view; kitchen fitters occasionally perform this trick when a kitchen gets re-modelled. If the wall has been re-plastered, only the householder's knowledge might help with identifying the location of any redundant accessory that was removed. Sometimes moving the sockets up to 4ft above floor level gets them out of the damp zone. Sometimes, a surface box is better than a flush one for a damp wall. Possibly a nail in the wall has gone into a cable (the RCD should trip for this). All a bit of a PITA. Regards,
Colin Jenkins.
 

Reply to Damp problems in sockets... solutions? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables. I have seen the pitch oozing...
Replies
9
Views
4K
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
915
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
821
Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock