LlandrilloSpark

Evening fellas

halfway thru an inspection on a 11 room hotel, found quite a few C1 & C2 but was wondering about this:-

In the main entrance hall there is a "fuse box" about 7ft from the floor level, i use the term fuse box lightly, it contains 5 porcelain 15A fuses, it has no main switch and is fed from a 32A BS3036 6ft below, the "cover" to this unit is wood and maybe original to the building (1894), the cover stays shut with a loose hook of sorts, there is no bus bar cover.

Is this another C1 as there is access to live parts...without a tool?

cheers
 
Reach down Guitarist, reading the post the feeding CU is 1 ft off the ground.
Llandrillo, I think you answered your own question mate, just before you said cheers:)
 
Evening fellas

halfway thru an inspection on a 11 room hotel, found quite a few C1 & C2 but was wondering about this:-

In the main entrance hall there is a "fuse box" about 7ft from the floor level, i use the term fuse box lightly, it contains 5 porcelain 15A fuses, it has no main switch and is fed from a 32A BS3036 6ft below, the "cover" to this unit is wood and maybe original to the building (1894), the cover stays shut with a loose hook of sorts, there is no bus bar cover.

Is this another C1 as there is access to live parts...without a tool?

cheers
well it could be construed as nothing more than `placing out of reach`....in an area woth unskilled/uninstructed persons....whatever it aint secure is it...so theres barriers n enclosures n all.....
 
I'd consider rotting rubber cables in a kindling box a potential fire hazard....are the neutrals fused?


Alternately it could be a display piece, current place Im working in wants one of them put back for show :smile5:
 
Reach down Guitarist, reading the post the feeding CU is 1 ft off the ground.
Llandrillo, I think you answered your own question mate, just before you said cheers:)

You're right trev, read it the wrong way.
Llan, you definitely answered your own question there mate :)
 
I'd consider rotting rubber cables in a kindling box a potential fire hazard....are the neutrals fused?


Alternately it could be a display piece, current place Im working in wants one of them put back for show :smile5:
i had one kicking about a while back....little 4 way with a glass paneled door on the front....the fuse carriers were long, thin white porcelane....probably dated from the 20s-early 30s.....i think i slung it though together with other crap.....
 
"it has no main switch and is fed from a 32A BS3036 6ft below, the "cover" to this unit is wood and maybe original to the building (1894), the cover stays shut with a loose hook of sorts, there is no bus bar cover."

One foot from the floor, in a box held closed by a hook with no bus bar cover! Code 1 all day long mate. How long would take for a child in a lobby of a hotel to stick their fingers in that after they work out how difficult a hook is to open.

No win, no fee written all over this one I think.
 

Reply to Dangerous or not?! in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock