Discuss Dangerous voltage to earth in the Canada area at ElectriciansForums.net

J

jonboy1

Just been to see a job in a block of flats. There was a flat that had had a leak and this has caused 3 other flats to blow there re-wireable fuses. The flats were supplied from a riser cupboard in VIR cable circa 1930's and VIR cable was run to each flat. The cables were in a terrible condition.
The fuseboard had what appeared to be 8 porcelain fuses running across the top level and 8 fuses on the bottom level all re-wireable. I believe the top level was the phase and the lower level the neutrals. I checked the voltages from phase to phase at the top and they all appear to be on the same phase. I also checked from the phase to the metal tubing coming up from riser which gave me 240V. The unerving reading came from the neutral to this metal pipe which read 380 V.

I suggested that i would come back and carry out insulation resistance test on the three cables running to the other flats to see whether the water had got into the cables below floor but really i do not like the idea of re-connecting/changing fusewire, even if they are ok when they are in such a poor condition and with this very alarming reading.

Questions:

Why am I getting this reading?
Does the neutral just need earthing correctly and what are the risks of carrying this out.
Should I just refuse to re-connect old VIR cables (tennants living in flats)
If i do re-connect what am I responsible for and can i just write out the bad stuff on limitations.

Really appreciate feedback.
 

Reply to Dangerous voltage to earth in the Canada area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
503
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock