im doing inspection on flats and ive came across
all 61900 type c rcbo ive recommended changing to type b
due to type c for inductive loads . could cause overload
what is the general opinon on type c on domestic?
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
G

Guest123

  • Thread Starter Thread Starter
  • #3
Hey Scott.

I'm a little confused by your post mate, a C type merely copes better with a high start-up current than a B type, and as it's an RCBO the breaker type isn't really an issue.

I believe wylex and crabtree only make their RCBO's in C type.

Can you elaborate on your "could cause overload" statement please.

Cheers
 
Last edited by a moderator:
S

Spudnik

  • Thread Starter Thread Starter
  • #4
I take it you mean 61009?

As long as your Zs is within the lower limits of a type C then i dont see a problem at all.

In fact, some manufacturers dont even make B type RCBO's.
 
Last edited by a moderator:
J

johnnyb

  • Thread Starter Thread Starter
  • #5
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.
 
D

DanBrown

  • Thread Starter Thread Starter
  • #6
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.
Our house has just been rewired by southern electric, with all type c rcbo's and nic'ed... Ther's nothing wrong with type c breakers so-long as the zs is still met..
 
J

johnnyb

  • Thread Starter Thread Starter
  • #7
I wonder why they do that Dan, Agree with the zs part, but i would bet that the majority of domestic premises are type b, don,t you think.
 
D

DanBrown

  • Thread Starter Thread Starter
  • #8
I wonder why they do that Dan, Agree with the zs part, but i would bet that the majority of domestic premises are type b, don,t you think.
I also agree with you that the majority of domestic are on type b breakers, but really does it matter type b or c?, i don't really think it matters, and as far as a danger - well, i dont think so ...
 
i think for all of us who understand that type c have half the max permitted eli of a type b it doesnt matter, but not everyone realises this and that is where the risk is,( know your max eli and all is well)
 
J

johnnyb

  • Thread Starter Thread Starter
  • #10
Never mentioned it was a danger Dan.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #11
Chaps,

The MAJORITY of manufacturers do not even make B type RCBO's as there is no real reason to.

The C type covers all installations, provided that the EFLI is within the maximum permitted. (or 80% corrected)
 
J

johnnyb

  • Thread Starter Thread Starter
  • #12
Sorry boys i was just on about normal type breakers, not rcbo,s.
 
M

maddfridge

  • Thread Starter Thread Starter
  • #15
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.
hi there

type c are used a lot in some lighting appilcations such as display lighting, air con etc but they are also used to give a bit more before all the lovely 3 kw fan heaters are connected in the office when the heating breaksdown lol:rolleyes:

cheers
 
D

DYCHE4230

  • Thread Starter Thread Starter
  • #16
Hi

Am I reading this correctly?

Page 44 OSG table 7.1.

On a ring circuit for a TNS system, No RCD, 2.5/1.5 T+E
A "type C rcbo" is not permitted ZS being the prohibitive factor?

Thanks
 
K

kung

  • Thread Starter Thread Starter
  • #17
Thats what i read on 32A ring not permitted by ZS but ok on 6A lighting same for RCD & NON-RCD
 
Last edited by a moderator:
S

Spudnik

  • Thread Starter Thread Starter
  • #18
Not really sure why a 32A RFC would ever need a c type to be honest.
 
D

DYCHE4230

  • Thread Starter Thread Starter
  • #19
Its not a case of needing one its a case that some manufacturers dont do b types so it would be useful if a c type was permitted.......

for instance I am doing a kitchen and the location of the CU makes it desirable to put in a RFC just for the kitchen..the previous electrician decided to put in a 16th split board and put the only ring and both lighting circuits on the rcd side. (niceic registered and told the customer he had done it to 17th regs????) so all lights and power on same rcd....I thought one solution would be to put kitchen ring on uprotected side on rcbo, but board is wylex and the b types rcbo's are hard to get hold of
and as discussed it appears that c types are not permitted for this type of circuit:confused:
 
S

Spudnik

  • Thread Starter Thread Starter
  • #20
You will also notice that it does not permit C type MCB's either although this is mainly for TNS systems.

Im trying to find info in the BRB with regards to this.

It just doesnt seem right to me.



Well looking in the BRB it gives EFLI values for type C MCB's and RCBO's so im not really sure what the OSG is on about.
 
Last edited by a moderator:
D

DYCHE4230

  • Thread Starter Thread Starter
  • #21
Your right Jason it does give ELI figures, although they are low, but still if your readings are less then I don't see the problem either?? maybe someone can thro some light on this as the OSG says that the prohibitive factor is the Zs???????
 
N

NickJPalmer

  • Thread Starter Thread Starter
  • #22
Hi,
Just bought 3x Wylex type B RCBO's online from Gil-Lec. Previously I contacted Wylex (via Electrium online) to find out if they still manufacture type B's and they replied that they do.

Hope this is helpful.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #23
Hi,
Just bought 3x Wylex type B RCBO's online from Gil-Lec. Previously I contacted Wylex (via Electrium online) to find out if they still manufacture type B's and they replied that they do.

Hope this is helpful.
Hager also still make b types. Just fitted a few.
 
P

Plan

  • Thread Starter Thread Starter
  • #24
One good thing about type c rcbo or mcb in a domestic lighting circuit because of it's higher tolerance doesn't always trip when a lamp blows.
As for the zs cos it's a rcbo the maximum allowed shoots up to 1666 ohms and if your measurements are that high debating between type b and c would be the last thing on my mind!
 

scotsparky

-
Arms
AS its an rcbo and therefore an RCD with overcurrent as long as it complys with Ib<In<Iz for the overload and the RCD complys with ZsIdn<50v then shurely its ok?
 