EICR installation 40 + years old… cabling PVC T&E… no MBPC…
As stated fuses, all ELI measurements are ok… RCD separate from DB/CU 30ma, what’s your feelings on a new DB/CU, installation is in a fair condition.
Classification code recommends C3
 
Well it is adequate by the key operational aspects (assuming bonding fixed).

However, I don't really like rewirable boards as not that many folks can safely rewire said fuse, both the act of changing the wire for more of the correct rating, and not attempting to remove/insert one in to a live board. In the past I would put in the Wylex plug-in breakers instead as a quick and approved means of avoiding that pitfall.

You could make a case that a CU upgrade would bring some improvement in safety on that front, along with SPD to reduce the risk to any fancy equipment, but it is still a C3 code so really more of advice for the future (e.g. if any new circuit needed, etc).
 
As far as an EICR goes if it is in satisfactory condition for continued use then that is what goes in the report.

But that doesn't stop you from discussing the merits of upgrading with the customer.
 

Reply to DB/CU Wylex 3036 6 Way in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be...
Replies
40
Views
4K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock