Does anyone regularly use or know of a suitable way to relocate a DB from its original position (adjacent to main fuse) if there is nowhere within 3m of the main fuse inside the building where a fused isolator can be fitted?

Main fuse is in an external meter cabinet, current DB position is on the other side of the wall, new DB position is to be 10+ metres away.

Is there a surface mounted external box which can be fitted in which a fused isolator can be installed inside?

Is there another way of fitting it internally which is still acceptable?

Thanks.
 
can yo not fit a KMF in the meter cupboard?
 
You can usually squeeze a KMF into the meter box
 
There are 2 x meter setups inside the meter cabinet so no room for much else!

Looking like a external surface mounted meter cupboard could be the way forward.

Any harm in drilling through the back of the meter cabinet and through the wall, then bringing the tails through the wall, into trunking taking them up into a suspended ceiling and fitting the 80/100A fused switch up there?

Would need to be a decent sized metal switch though to take a 25mm SWA away me thinks.
 
There are 2 x meter setups inside the meter cabinet so no room for much else!

Looking like a external surface mounted meter cupboard could be the way forward.

Any harm in drilling through the back of the meter cabinet and through the wall, then bringing the tails through the wall, into trunking taking them up into a suspended ceiling and fitting the 80/100A fused switch up there?

Would need to be a decent sized metal switch though to take a 25mm SWA away me thinks.
why SWA if in trunking?
 
if tails are> 3m then fusing down to 80A makes sense, protecting the DNO fuse. have you opened it to check that it is what it says on the tin?
 
I usually drop the downstream OCPD to 63A for a 100A main fuse. I think 80A is too close to ensure that this will blow first. I thought there was something in the regs about this, but I can't find it with a quick flick through... maybe someone with a soft copy can find it ?
 
For BS88 fuses you typically need a 1.6:1 ratio for selectivity, so basically two "steps" in the rating (e.g. 63A and 100A, or 50A and 80A, etc).

However, here the only reason for putting in the fuse is to satisfy the regulations that say it must have its own OCPD if over 3m unless the DNO agrees to their fuse being used (assuming the SWA is OK for the DNO fuse rating obviously).

So you don't need selectivity here. You are not running a supply with multiple circuits off it so they need to be able to disconnect independently, and you are not running any sort of load that can be expected to blow it (e.g. some massive commercial motor, etc).
 
"So you don't need selectivity here. You are not running a supply with multiple circuits off it so they need to be able to disconnect independently"

What do you mean by this? Don't know if im taking what you're saying too literally but the supply will be feeding a DB with multiple circuits off it?

With Telectrix asking why SWA if ran in trunking, is there a not a limit to how far meter tails can be ran if enclosed in trunking? This would probably be easier than trying to find a KMF that will allow for a 16mm/25mm SWA to be glanced into it in a tight spot?

I've seen it before where tails are ran over a distance of 10-15m above a ceiling but running single cores over that distance doesn't seem very well protected.
 
What do you mean by this? Don't know if im taking what you're saying too literally but the supply will be feeding a DB with multiple circuits off it?
I mean you are not taking multiple fused sub-mains off the DNO fuse (not a Ryefield board or similar where you would expect selectivity between multiple supplies).

The CU with multiple circuits is very unlikely to blow the DNO fuse. Typically you have assessed the expected total demand allowing for diversity and real world use. So while the sum of MCBs probably far exceeds 100A, many will never be run at maximum (e.g. lights at 6A per floor, etc), and others like RFC are rarely running at their limit.

Without the sub-main you would not be putting in a fuse to protect the DNO's fuse, so with a single sub-main simply extending it then the same surely applies?
 
With Telectrix asking why SWA if ran in trunking, is there a not a limit to how far meter tails can be ran if enclosed in trunking? This would probably be easier than trying to find a KMF that will allow for a 16mm/25mm SWA to be glanced into it in a tight spot?
If the tails are mechanically protected and so unlikely to be damaged by DIY nailing of stuff to walls, etc, then you don't need SWA.

Often on here you see questions about long tails with just an isolator and not a switched-fuse, and it comes back to the same "3m rule" and if the DNO fuse can be considered acceptable OCPD for the installation.
 

Reply to DB to be located away from DNO equipment in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
535
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
790
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock