Hi guys
Is it possible to use 2 strings through one isolator. For example 2 no 820v strings..trying to clear up a disagreement. 1000v isolators used. Thanks in advance and when is 3rd edition of the pv guide coming out ???
 

SolarCity

Electrician's Arms
Solar Guru
Messages
4,094
Yes, you can. Personally I would use two isolators, but there is nothing wrong with using one for two strings.
 

moggy1968

Regular EF Member
Messages
1,836
yes you can. IMO do a 4 pole DC isolator for 2 strings which also doesn't use interconnectors to get seperation.
Siberts do them
 

Gavin A

Electrician's Arms
Solar Guru
Messages
4,238
Location
Leeds
Hi guys
Is it possible to use 2 strings through one isolator. For example 2 no 820v strings..trying to clear up a disagreement. 1000v isolators used. Thanks in advance and when is 3rd edition of the pv guide coming out ???
as long as it's within the manufacturers specs - k&E have a sheet on their site that details the specs for each isolator for single and 2 strong operation - we always give it plenty of leeway with them, if in doubt use the next size up (technically I believe ampage & voltage +20% is the recomendation)
 

moggy1968

Regular EF Member
Messages
1,836
Pay careful attention to the wiring diagram for this item. The first time we used one lets just say we didn't!!
yes, we nearly fell for it! Fortunately I'm in the habit of reading the instructions on any new item even if it looks straightforward, and also buzzed it through to confirm (people do look at me a bit odd sometimes when I sit reading the instructions for a bathroom light, but sometimes it pays dividends! Actually, maybe they are just looking at me a bit odd for other reasons!)

It's logical enough when you realise whats going on.

I posted a thread about it on here a while ago
 

Worcester

Mentor
Electrician's Arms
Solar Guru
Trainee Access
Messages
3,647
Location
Worcestershire
We have used the four pole ones from IMO (Andy at Sibert) however despite it appearing to save money / time on installs we've gone back to using one isolater per string. - Reason, it makes maintenance and fault finding a lot lot easier. We have lots of sites out there with 15 - 30 strings and halving the number of isolators seemed like a good idea, so despite using them I still remain to be convinced..
 

moggy1968

Regular EF Member
Messages
1,836
I haven't done any installs that big but it hasn't been a problem, in fact it made things easier when we had a string not outputting, only one cover to take off! It savers space time and money so on double strings I always use them. Maintainance hasn't been an issue, as there hasn't needed to be any.
 
OP
S

Scrag

Active EF Member
Messages
27
Location
Torba
Thank you for replies. Been away working and have just gone online.
That clears that one up
 