Hi guys
Is it possible to use 2 strings through one isolator. For example 2 no 820v strings..trying to clear up a disagreement. 1000v isolators used. Thanks in advance and when is 3rd edition of the pv guide coming out ???
 
yes you can. IMO do a 4 pole DC isolator for 2 strings which also doesn't use interconnectors to get seperation.
Siberts do them
 
Hi guys
Is it possible to use 2 strings through one isolator. For example 2 no 820v strings..trying to clear up a disagreement. 1000v isolators used. Thanks in advance and when is 3rd edition of the pv guide coming out ???
as long as it's within the manufacturers specs - k&E have a sheet on their site that details the specs for each isolator for single and 2 strong operation - we always give it plenty of leeway with them, if in doubt use the next size up (technically I believe ampage & voltage +20% is the recomendation)
 
Pay careful attention to the wiring diagram for this item. The first time we used one lets just say we didn't!!

yes, we nearly fell for it! Fortunately I'm in the habit of reading the instructions on any new item even if it looks straightforward, and also buzzed it through to confirm (people do look at me a bit odd sometimes when I sit reading the instructions for a bathroom light, but sometimes it pays dividends! Actually, maybe they are just looking at me a bit odd for other reasons!)

It's logical enough when you realise whats going on.

I posted a thread about it on here a while ago
 
We have used the four pole ones from IMO (Andy at Sibert) however despite it appearing to save money / time on installs we've gone back to using one isolater per string. - Reason, it makes maintenance and fault finding a lot lot easier. We have lots of sites out there with 15 - 30 strings and halving the number of isolators seemed like a good idea, so despite using them I still remain to be convinced..
 
I haven't done any installs that big but it hasn't been a problem, in fact it made things easier when we had a string not outputting, only one cover to take off! It savers space time and money so on double strings I always use them. Maintainance hasn't been an issue, as there hasn't needed to be any.
 
Thank you for replies. Been away working and have just gone online.
That clears that one up
 

Reply to Dc isolators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock