I am after a bit of advice if anyone can help. I got called to a job due to RCD tripping. Ir circuits and fault was on cooker. Disconnected cooker and fault gone from DB. The landlord tried to get the cooker fixed , but appliance engineer couldn’t fix, so he brought a new cooker. Today he had cooker installed but when it was switched on it tripped the rcd. I went back and the cooker was disconnected and I found no fault from the DB, however when I did an ir from switch back to DB I had a dead short neutral to earth. It’s a flat so can’t pull boards up from upstairs so am going back to run a new leg of cable. Has anyone got any idea why it would show a good ir from DB to switch but not the other way around.
Thanks in advance
Steve
 
If the cable is continuous the IR will measure the same from all points. If the cooker worked we can assume the neutral is continuous, but did you check the CPC continuity? A nail or screw through the cable could just possibly sever the CPC and short the switch side of the break to the N, leaving the DB side disconnected.

Another explanation is that the fault is intermittent and located near the switch, where any movement of the cable can make or break the contact. It actually reads the same IR from both ends at any one moment, but the act of opening and moving the switch to carry out the test can provoke the fault to come and go, so you get different results each time you test.
 
Scenario: drill a hole through a cable due to muppetry, bang. Remove drill bit / screw = you now potentially have a broken conductor from the supply side and a shorted conductor on the load side.
 
Ah of course. Then when the cooker completes the circuit, the rcd detects the imbalance and trips. Makes perfect sense now. Thank you both for your replies.
 
If testing back towards the board, you need to isolate at the origin if testing between E and N.

remember that N is connected to E somewhere. For TNC-S it is connected at the property, for others it’s done at the substation, but they are always connected on the supply side.
 

Reply to Dead short neutral to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
354
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
762
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock