Discuss Dead Testing - 3Phase Motor and S-Plan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

W

whazza22

When testing Insulation Resistance or Continutiy on a 3phase Motor, do you need to disconnect the cables from the motor?

Or do you just test I.R to the starter, then I.R from starter to motor? (as the starter will be open when dead)

Would a motor come under "equipment vulnerable to testing" section on test sheet?

Also, when testing S-Plan system, do you test the I.R to the fused spur on 500v, then test each component at 250v? - How would you test continuity of S-Plan?


Help much appreciated
 
Personally I'd always have the cable to motor disconnected to do IR test; and rightly or wrongly only test up to the fused spur on central heating systems when doing a PIR. Initial verification I'd always carry out 500V IR on heating systems before terminating.
 
Last edited by a moderator:
Is that incase it messes up starter?

Can a 3phase motor be tested on 500v?

What about testing all central heating components on 250v only?
 
Last edited by a moderator:
your testing the motor windings so alway disconnect leads and any jumper bars, cant help with your s plan question though mate

(more info) i test at 1000v on a 400v supply but 500v is perfectly acceptable, for 1000v test you should read>1.4Mohm but will probably read off scale,>1Mohm
 
Last edited by a moderator:
Insulation resistance tests should be made on electrically isolated circuits with any electronic equipment which might be damaged by the test voltage disconnected.

If you cannot disconnect it you should connect line and neutral together and then test between your line and neutral and your cpc. You do not start just testing up to a fused spur and ignoring the rest of the circuit and you do not test at 250v instead of the required 500v dc test.

When testing a 3 phase motor you leave the motor connected to its supply cables and you disconnect from the overload in the starter. That way you include the supply cables as well as the motor itself. Again test at 500v dc NOT at 1000v.

Regards

Dichroic;)
 
Where do you you connect the line and neutral together? (not sure what you mean)

So, for a motor you disconnect both sides of the starter and connect them in connector blocks, then test?
 
Insulation resistance tests should be made on electrically isolated circuits with any electronic equipment which might be damaged by the test voltage disconnected.

If you cannot disconnect it you should connect line and neutral together and then test between your line and neutral and your cpc. You do not start just testing up to a fused spur and ignoring the rest of the circuit and you do not test at 250v instead of the required 500v dc test.

When testing a 3 phase motor you leave the motor connected to its supply cables and you disconnect from the overload in the starter. That way you include the supply cables as well as the motor itself. Again test at 500v dc NOT at 1000v.

Regards

Dichroic;)

the op was asking about testing a 3ph motor, not a 3 phase motor and cables to a 3ph motor, and by all means set to 1000V as its a more thorough test
 
the op was asking about testing a 3ph motor, not a 3 phase motor and cables to a 3ph motor, and by all means set to 1000V as its a more thorough test



Sorry PMAC silly me!! Lets test the motor and hope the supply cable is fine. What was i thinking ??:D

Oh and lets test the motor at 1000v dc and give it a thorough rogering on its laminations before we start it up :eek:

Dichroic
 
does supply current and FLA mean anything to you:confused:
what if the motors a long distance fom the starter? where do you begin to fault find?
excess current damages windings in a ac motor, not dc voltage,

im thinking were talking different environments here, i test motors on an factory sight when i suspect a motor fault not routine testing, these motors may also be marked 415/660V and are delta connected, ill agree to disagree, but i work on the advice of a rewind specialist whom i send my faulty motors to
 
Last edited by a moderator:

Reply to Dead Testing - 3Phase Motor and S-Plan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
392
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
617
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
955
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock