I'm doing an design project at college and are onto my cable calcs now and I'm fine with my lighting circuits and the fridge and dishwasher supplys where the load has been stated but I'm confused as what to do about my socket outlets as in the spec there is nothing specified about the socket circuits. How do I work out the design current without knowing the load or do i just leave the box blank or N/A for my socket circuits? I don't know what will be getting plugged in to these circuits at all and there hasn't been anything specified.
 
The thing with sockets is they can all be loaded up under the end user's control, not the circuit designer's control. So when you design the cable and OCPD to feed the sockets you generally have to assume the worst possible case. So whether you go for a RFC in 2.5mm, or radials in 2.5mm or 4mm, etc, you have to make sure the OCPD does not exceed the thermal limit (CCC) of the cable as installed.

However, you also have the end use problem and that is where you have to consider if the available socket are able to power all of what the user can reasonable expect to have fitted. In practice you can allow for a bit of diversity.
 
The thing with sockets is they can all be loaded up under the end user's control, not the circuit designer's control. So when you design the cable and OCPD to feed the sockets you generally have to assume the worst possible case. So whether you go for a RFC in 2.5mm, or radials in 2.5mm or 4mm, etc, you have to make sure the OCPD does not exceed the thermal limit (CCC) of the cable as installed.

However, you also have the end use problem and that is where you have to consider if the available socket are able to power all of what the user can reasonable expect to have fitted. In practice you can allow for a bit of diversity.
ok thanks pal
 

Reply to Design current of socket outlets in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Im currently in my apprenticeship and completing an assignment that involves cable calculations. Im currently stuck on how to find the design...
Replies
1
Views
484
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hello, I’m currently at college doing a design project which is based in a hotel/swimming pool area. I have been given an example but it doesn’t...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock