Is it common to get different test results when upgrading a db? Basically I done an EICR in November and came back to upgrade the db and done live tests on all the circuits, but my results were quite different. Like 0.30 ohms out on one circuit
 
Tested before, during initial EICR way last year. Then went back to upgrade DB this week and we live test after upgrading DB, the Zs readings on some circuits were a lot lower than they were. Meter tails were upgraded and the Ze went down by 0.11 but some circuits the Zs was 0.30 lower
It might simply be a result of re-terminating all the CPC's properly.
Does it happen to be the case that the ring final circuits are closer to original readings? In theory these will have had the CPC disconnected for fig 8 tests, so should be more recently tightened.
For other circuits it's conceivable that the CPC's weren't touched during the EICR...depending on how the tests were carried out of course.

Then again live Zs tests are notoriously variable and can be affected by electrical 'noise' easily.
 
It might simply be a result of re-terminating all the CPC's properly.
Does it happen to be the case that the ring final circuits are closer to original readings? In theory these will have had the CPC disconnected for fig 8 tests, so should be more recently tightened.
For other circuits it's conceivable that the CPC's weren't touched during the EICR...depending on how the tests were carried out of course.

Then again live Zs tests are notoriously variable and can be affected by electrical 'noise' easily.
Like you say could be a combination of that, and the fact the ze is went down by 0.11 since the tails have been upgraded etc
 
It might simply be a result of re-terminating all the CPC's properly.
My money is on this possibility or something similar. For instance, we have recently had to carry out testing on premises that were dormant/vacant for 2 years (covid related). A number of FLi socket circuit tests were marginally higher than the regs allowed. I did wonder why the installation had been passed in the first place. However as the installation opened up for business again and sockets started to be regularly used we found on retesting some weeks later that Zs values had dropped significantly. Sometimes it can be as simple as a fine film of dust lying on the contacts
 
Of course if you get a high reading on a socket, the usual thing to do is to put the plug (tester plug top) in and out of the socket several times
Yes. That's what would normally be done on getting a high reading. And that's what we did on initial testing, but it did, nt bring the readings down. It was only after several weeks of the sockets been in continuous use that that there was an impact on the readings. I, m just speculating that the long dormant period led to this situation somehow
 
A lot can depend on the environment the MFT was kept / transported to site in prior to the testing being carried out and if it was given time to acclimatise to the conditions of the premises being tested

This is one of the reasons why I'm not a fan of wholesalers on the day calibration events as it is difficult to produce accurate calibration results without the lab conditions to give a baseline to qualify the results to the required standard
 

Reply to Different test results after DB change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
768
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
600
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock