Just started with the continuity test on a domestic installation prior to a board change. Its only a small property and all the sockets are on one ring cct, a grand total of 10 sockets. I did the phase and neutral and they both came in at about 0.5 ohm but the cpc was open circuit. I've followed it all around the house and the break appears to be between the kitchen and the rest of the house. The problem is that the (i suspect ) dodgy junction box is in the kitchen ceiling. The kitchen is an extension on the back of the house and has its own pitched slate roof, with no access to the ceiling void.
The question is do I investigate further or just bite the bullet and split the ring into two radials?
I have I/R'ed the cpc and it gives a reading of 0.01Mohms at 10v ( i'm using a fluke 1651b).
Any thoughts anyone?
 
Yes it appears to be between the first socket in the kitchen and the last socket in the front room, if that makes sense. The ring goes from the board into the front room where there are four sockets with legs upto one socket in each of the two bedrooms then back into the kitchen to four sockets and back to the board.
the problem is that I cant find where the ring enters the kitchen. Ive had the floor boards up in the bedroom and all the cables are intact before they disappear through a small hole in the wall and into the kitchen ceiling void.
 
Why would there be a junction box in the ceiling void? Are all the sockets in the kitchen on the ring or are there some spurs.
 
There are no spurs, the junction box in the ceiling void is the only thing i could come up with for the readings. It's just me clutching at straws.
 
Sound like when they built the extension, they may have added this to the existing ring and like the OP said, used a JB somewhere to join it.

If you are sure its in the ceiling void, explain to the customer the pros and cons of splitting and making 2 radials and knocking a hole in the ceiling to fix.
 
Does the CU have capacity for an extra fuse/mcb allowing you to split the circuit? If not would it be acceptable to add a CPC link from the "2" offending sockets so that the CPC is then a "ring"?
 
get a dade, a 110mm cutter and cut a hole in ceiling above the suspect sockets. Rattle the cables to get an idea of where the joint might be.........after you find/sort it. Fit a batten across the hole then screw back the cutout and fill the gaps............my customers love this one and it leaves the job sorted and i find the joint after about 4 holes ............usually.
 
I'd opt with a JB and not a damaged cable, as CPC is in middle of cable - a screw through it would probably still offer some continuity reading and prob reduce IR readings.

Classic case of why all terminations and connections should be accessible at all times I suppose.

If you're going to run a CPC single between the two sockets then you might as well run a full 6242Y. The damage won't be much different.

Two rads: test results, loads on each rad, and space in c/u permitting
 
I had a fault on a existing ring main, i installed an extra socket and found there was no continuity on the cpcs when testing. Located the faulty wire to be between two sockets in the lounge, found a jb with a spur but all connections were ok, after a bit of head scratching the break was found to be caused by a nail in the skirting board! i have to add the original nail from when the house was built 40yrs ago. It was worrying that this fault had never been picked up in 40 yrs, just goes to show the importance of testing every circuit you work on.
 
I know its changing the focus here but get yourself one of them snake scopes ! makes life so much easier buddy ! Maplin do them cheap.
 
Yes buddy ! they do both and might be on sale at mo as they have a big sale advertised i had emailed to me ! the reason i have the laptop required one is so i can take pics and vids with it as comes in handy with PIR's and you can see the pictures bigger on laptop screen also you dont have to see the lcd screen if you have your hand under a floor etc as with the other hand held one with the lcd screen but that one seems ok to. Ive used it to look down cavities, in ceilings & under floors that you can get away with most of the time just lifting the floor boards a few inches one end ! also behind kitchen units etc etc great must have time saver etc for little money.
 
At Maplin they are £39.99 at the moment, slightly cheaper on ebay.

Can't believe they are so cheap now - will flex my credit card tomorrow!
 

Reply to disappearing earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
975
Hi, I've got a light with a ceiling rose in the kitchen. While rectifying some faults in the house I came across to the light and measure Neutral...
Replies
25
Views
5K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock