ok this q come up in college. And we couldn get to a conclusion.

Max dis time : 0.4s......

TT system , not possible ( high Ze).

So must have rcd to obtain 0.4s...rcd testing , : must operate in 0.4 s @ x 5 current.

However bs7671 states disconection time for TT system as 0.2 secs ? ( portable equipment) .

Why isnt the rcd time for TT 0.2 secs @ 5 x current ?
 
ok so basically its this? :

times : 0.4 for TN : 0.2 for TT .

So TT : 40 ms for rcd @ 5 x current ( 0.04) < 0.2 (200) ? Yes, 40ms < 200ms; 415.1.1

For non RCD protected circuits, faults to earth are 0.4s (400ms) for TN, 0.2s (200ms) for TT; Table 41.1, so yes, your're right there.

With RCD, @ 1 x In, clear fault within 200ms, TN or TT (someone check that for me!)

(BRB refs)
 
For non RCD protected circuits, faults to earth are 0.4s (400ms) for TN, 0.2s (200ms) for TT; Table 41.1, so yes, your're right there.

With RCD, @ 1 x In, clear fault within 200ms, TN or TT (someone check that for me!)

(BRB refs)

Yeah : 1In 200ms : 5In 40ms ....i think . ...ok , cant believe nobody in college picked up on tha...lol
 
And the next question is "how does an RCD to BS 61008/61009 comply with a 0.2 second disconnection time?"

The answer is in the note at the foot of table 41.1 and then the additional time/current figures for RCD's in Appendix 3 of BS 7671
 

Reply to Disconection times in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K
Hi all, just a quick one regarding RCD disconnection times. So for non rcd protected circuits disconnection times of 0.4 / 5 seconds and 0.2 /...
Replies
11
Views
5K
I was asked to go and take a look at a generator set up by a marquee company yesterday to do some testing. It was a brand new JCB 65QS with...
Replies
7
Views
2K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock