I'm having a bit of a brain fog moment (changing medication is such good fun!) and am looking for confirmation that I'm either right or talking nonsense.

I've been to a job to have a look at why a set of ammeters aren't working, I've established the main reason they don't work is that someone has disconnected them, pretty simple so far.

But the CT's which fed these ammeters have been disconnected and left open-circuit, I'm pretty damned sure they should have been either shorted out or removed and that's what I'm looking for confirmation of.


And the second question how would you code this on an EICR? I would give it a C2 as it is behind a panel on a switchboard but is a set of terminals with, potentially, a 4 figure voltage between them.
 
I agree, an open circuit CT can have some big voltage’s across the terminals.
I would not be hooking them back up until I confirmed that the cable is carrying no current.
 
Its a good question, i think you can code it a number of ways but C2 would be a good start. Having higher voltages than the cable was designed for is a good start, obvious shock potential for anyone trying to fault find and fix. Sometimes though, for the sake of it, i sometimes just fix it , there and then. Any chance of just linking them out or at least if the Cts are clip ons, just remove them, (quiet time obviously)
 
Its a good question, i think you can code it a number of ways but C2 would be a good start. Having higher voltages than the cable was designed for is a good start, obvious shock potential for anyone trying to fault find and fix. Sometimes though, for the sake of it, i sometimes just fix it , there and then. Any chance of just linking them out or at least if the Cts are clip ons, just remove them, (quiet time obviously)

We're booking in an out of hours visit for a full shutdown to fix some serious nasties and I'll sort this out while I'm there.

I'm not doing an EICR on this, someone else did and completely missed this despite spotting other issues behind the same access panel.

I agree with just fixing it and would have done that if I had been doing an EICR and had the supply isolated at the time.
 

Reply to Disconnected CT's and EICR coding in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Morning, Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking...
Replies
22
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
674
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock