V

vlevente

hi
our electrical company permits the installation of the inverters that have some delaying in reconnection to the grid.
example: if no power on the grid(maintenance), the inverter must not feed to grid so that no injuries can occur if are electricians working.
can anybody tell me a few inverters that has this kind of specifications?

thanks
 
You are actually meant to test it yourself (no one does) but your meant to turn off the AC isolator and time how long it takes the inverter to turn off (to comply it needs to be less than 5 seconds) there is no machine to do this, but in the electrical world 5 seconds is a long time and they should turn off in less than 1 second (you can easy do this by eye)
 
You are actually meant to test it yourself (no one does) but your meant to turn off the AC isolator and time how long it takes the inverter to turn off (to comply it needs to be less than 5 seconds) there is no machine to do this, but in the electrical world 5 seconds is a long time and they should turn off in less than 1 second (you can easy do this by eye)

You sound like a sparky who used to work for us!

We do all the PV tests. It doesn't take long to do them all and I usually have them all done by the time the rubbish has been cleared up - which is a job I hate anyway!
 
If you haven't conducted all the tests, with appropriate results, then you shouldn't be signing the system off as G83 compliant and submitting it as such to the DNO.
 
How can you sign this document (old one I know :) ) without doing the test?

Fullscreen capture 13122012 091236.bmp.jpg
 

Reply to disconnection/connection to on-grid-time wait in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
903
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
1K
Hi. We live in an older house and we are doing a loft conversion. We do not have an SPD on the connection to the grid and the builder's...
Replies
49
Views
5K
So despite living working in a country blessed with 300 days of sunshine I have not got my head around this solar thing, there is very few...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock