Discrimination | on ElectriciansForums

Discuss Discrimination in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 1, 2024
Messages
2
Reaction score
1
Location
Earth
First post - Go easy!

Advice please - suggestions/best practice.

Domestic property, TNCS supply, 25mm tails to RCBO C/U with 100A main switch.

I want to install a distribution circuit from the aforementioned C/U (I dont want to split tails) to supply a second RCBO C/U (essentially a garage board), serving little more than a lighting and power circuit.

The cable supplying the second board is 10mm T&E and already buried within the fabric of the building and will be used (non negotiable).

with discrimination in mind, what device should I be terminating the 10mm distribution cable, within the second board?

I am using Fusebox boards and the smallest main switch I can see is 63A. This is too big for the 10mm supply cable???

Any advice warmly recieved.

 Thanks
 
How did that user name get past the software filters?
If you’re trainee, as profile says, then @Dan can badge you as such


The 10mm cable is protected at the house end by a suitable sized rcbo….

The mainswitch at the garage is just a switch…. Not an overcurrent protection device.
 
How did that user name get past the software filters?
If you’re trainee, as profile says, then @Dan can badge you as such


The 10mm cable is protected at the house end by a suitable sized rcbo….

The mainswitch at the garage is just a switch…. Not an overcurrent protection device.
Blimey - that was painless (I anticipated an onslaught of responses).

Thanks Littlespark - appreciated.

Noted re the trainnee forum - I will move over there.

Download virusđź‘Ť
 
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes.


Things to think about with the proposal though... You have a 10mm T&E existing... protected by rcbo... which it may have to be depending on how its run.
You would then not technically need rcbos on the outgoing circuits from the second CU, as the supply would be rcd protected anyway.
 

Reply to Discrimination in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
511
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
752
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top