I wonder if someone can answer a question for me . We have to install a new dis-board in a property that already has a landlords distribution equipment installed . The landlords distribution equipment has its own service head and earthing arrangement . We wish to install a new supply taken from the tenets LV system which has its own service head and earthing arrangement some 45m away . The two systems will be sitting side by side . Do we need to ensure a distance because of the two different earthing arrangements ?
 
Speak to the DNO it is for them to specify. Most do not like secondary supplies to the same room. There is a danger that if the supplies are from separate transformers you could get circulating current through the neutrals/earths especially with PME supplies. Another danger is if there is any interconnection between the systems and one transformer is off supply due to a HV fault it would cause a back feed through the interconnection (for a short time anyway)
What you are suggesting is generally a very poor design anyway and trying to do the job on the cheap when you should be getting the correct supply installed.
 

Reply to Distance Between Supplies in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
522
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
989
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
446
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock