Hello people,
I'm designing switchgear for a residential estate, of about 60 houses, specifically the protection for the incomer. Is there any provision in the British Standard that advises on diversity for such a large number of household units?
In the UK most DNO's allow 2 or 3 kW per dwelling as long as there is no electric heating.
so 60 x 2 = 120. the next up standard size of transformer is 200kVA.
Can’t imagine electric heating will be a requirement on this one ?
No, but air-con may be an issue. I know the OP says that they use British standards but I think there will be a big difference between a standard UK house and a Kenya one.
Yeah, thanks a lot for this, the weather is not too extreme here and the cold and warm days are tolerable without electric devices.
I was thinking on the lines of say, NEC 220.84, if there's any document in the British Standards that may be an equivalent.
Reply to Diversity Factors in the Electrical Engineering Chat area at ElectriciansForums.net
Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Electrical2Go - Beginners Guide to Positive Input Ventilation (PIV) Units: A Solution to Indoor Air Quality Woes A guide to Positive Input...
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Hi all, I posted here some time ago asking for validation of a quote I received for a rewire. (10k assumed 60 points) And got some good advice so...