Hi all, have been to a bungalow (well half bungalow half building site at the moment) and the main supply is in the middle of the basement. The dno supply is coming from above so is hidden in a wall and then I can see it going through the loft to outside. It's a good 8 meter run. Has anyone come across this before? In my experience they are normally on the outside walls or at least underground if in the centre of a house. It just dosen't sit right to me, is there a depth in the wall that's acceptable? Surely not as the cable is not protected or fused down. Is this at all my responsibility from a legal standpoint? Surely it's the dnos. I can only guess that years ago the cable came straight into the house and at some point the house has been extended and they have built around the cable where it would have been on an outside wall, incorporating it into the building fabric. I'm reluctant to get the dno around as itll delay her other works and they will probably move the supply to an outside wall, making her incur costs to get the wiring moved. I would have thought if the whole build was finished I'd have never noticed or payed much attention to it, but I have so thought I'd ask, anyone with any experience would be great to have opinions. Cheers
 
Last edited:
I've not come across a DNO supply buried in a wall before, running through lofts and voids is common with overhead supplies but always accessible. I would agree that buried in a wall where it may be subject to inadvertent disturbance or mechanical damage it represents a real danger. Only option is to discuss with the DNO.
 
I would speak to the DNO but they must be prepared for a charge to rectify because it is highly likely as you say been concealed by building works. If anyone were to pierce the cable through DIY works you may have a serious situation as circuit protection is unknown.
 
Not protected by anything, it goes down in between an internal wall in the cavity between two red brick walls (which makes me think it used to be an outside wall).
 

Reply to Dno supply running through house in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
802
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
676
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock