Discuss DNO's incoming capacity. in the UK Electrical Forum area at ElectriciansForums.net

sparksburnout

-
Esteemed
Reaction score
1,766
Looking at a job where shower is required, and amongst all the other requirements, contacted the DNO to enquire what the incoming supply capacity is. The cut out fuse has no marking that states its rating, existing meter>CU tails are 16mm but will be using separate CU for shower circuit via henley block. It's like trying to contact Elvis, guys at DNO don't even seem to know what I am talking about. House is circa 1950's. Does anyone have any thoughts, whilst I am waiting, on the usual minimum capacity? Are there any domestic supplies that are likely to be less than 80 amps of this age? Are these DNO's (Wester power) usually pretty useless??
 
Will be either 60 or 80 amp DNO fuse. What problems are you foreseeing by adding this shower ?
Customer is not sure what size shower to go for, maybe I am being over cautious but everything else is electric and didn't want to get close to maximum demand. I understand diversity needs to be taken into consideration but quite likely they will have shower/cooker/fire/heaters on at same time, albeit it short period. Personally I can't see a problem, but I assume that "assessing the demand" has some relevance? Are there many/any cases where the DNO actually has to provide a new incomer for such situations??
 
bung in a 8.5kW shower. if the fuse blows, it blows. DNO's problem, not your's.
 
Customer is not sure what size shower to go for, maybe I am being over cautious but everything else is electric and didn't want to get close to maximum demand. I understand diversity needs to be taken into consideration but quite likely they will have shower/cooker/fire/heaters on at same time, albeit it short period. Personally I can't see a problem, but I assume that "assessing the demand" has some relevance? Are there many/any cases where the DNO actually has to provide a new incomer for such situations??

You will be right I would imagine, even on a 60A fuse. They won't blow at 60A anyway on a short period slight overload.
 
A few years ago a customer wanted an 9KW electric shower and also has storage heaters, I checked the main fuse and it was 40amp. The house was an ex council house built in the 1960's. apparently it was common then to fit smaller fuses. I called the DNO and they upgraded to 100amps, no bother.
 

Reply to DNO's incoming capacity. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock