about to wire 10 110v 16A single phase sockets in industrial building have been told they need double pole mcbs but do they need rcd protction rcbos is my easiest option as merlin board with conversion is special order any help appreciated
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
G

Guest123

  • Thread Starter Thread Starter
  • #3
Hey.

I have to say I do install RCD's/RCBO's on 110V circuits particularly for circuits supplying external equipment as Ian said.

Cheers
 
M

maddfridge

  • Thread Starter Thread Starter
  • #4
about to wire 10 110v 16A single phase sockets in industrial building have been told they need double pole mcbs but do they need rcd protction rcbos is my easiest option as merlin board with conversion is special order any help appreciated
hi there

big red book
page 181 section 704

regulation 704 410.3.10

i see this as what are you going to use the socket outlets for ?????


hope this point you in the right dierction

cheers
 
T

thomsonminis

  • Thread Starter Thread Starter
  • #5
industrial building mainly grinders and various othe hand tools
 

Reply to do 110v need rcd in the Commercial Electrical Advice area at ElectriciansForums.net