W
whazza22
Hi all
Replacing a consumer unit and I always upgrade the tails from the meter to 25mm.
However, the run is an absolute nightmare for a flat im doing a the meter is in the communal hallway.
I'm assuming they have to be upgraded if changing consumer unit?
Not if the DNO head is 60a.....or if you consider the load at present to be within the capacity of the existing tails.
The onsite guide recomends you do however remember that is just a guide, If the tails are in good condition and are covered by the main service fuse then id leave them in place. IE 100a gets 25mm
I usually allways fit new tails however if as you say its a pig of a job then providing that are large enough and in good nick then they can stay
I agree with wirepuller and bigbaddave.
If it's unpracticable to replace the tails then don't do it - providing they're adequate for the load.
The onsite guide is purely a "guide" and is mainly aimed at new builds.
Just imagine the size of the OSG guide if it covered all eventualities!!
besides most cases would involve the electric company to come and disc/re- connect to the meter - wouldnt it ;)
It'd be about the size of the BGB surely that covers absolutely everything :book:
The answer is NO, it's like asking do you have to replace the consumer unit if you are replacing the tails, why are you assuming they have to be upgraded? and why do you always replace existing tails with 25mm?
Hi all
Do tails HAVE to be upgraded?
Thread Tags
Tags Tags
tails
whazza22,
Engineer54,