Good evening all,

I need a sanity check and hoping you guys can help.

I'm currently working in Bournemouth upgrading a load of displays in bus shelters and the company who owns them have asked me to provide certs for our connections.

The problem I am having is that the last 10 shelters I have been to have no earth connection whatsoever.

I'll explain how they are wired.

The DNO has put their cut out underneath the poster panel in the bus shelter. These are TN-C-S supplies fed directly from the road. The incoming cable is a hybrid 2 core DNO cable, with an aluminium core and copper outer sheath that is for combined neutral and earth. I've watched the guys put them in before so it's definitely direct from the road.

The cpcs of the lights, poster panel and our bus departure sign are all connected to an earth stud and bonding is taken from there to other parts of the shelter.

Now the part I am concerned about. The earth stud on the shelter is not then connected back to the combined N + E terminal in the cut out, meaning the whole bloody shelter isn't earthed. When taking a ZS from my sign I have been getting readings from 45 ohms up to 180 ohms! These are protected by RCBO's so hopefully they'll kick in if there are faults in the lights and signs. (Although a lot of them don't trip in time / at all)

Surely I'm right in thinking that if there was a fault in one of the "tails" from the cutout to the RCBOs feeding the other circuits, for example the cables becoming trapped in the door or rubbing against the enclosure, then the whole shelter will become live. By my calculations at 180 ohms (230/180) means that you would only get a current of 1.2 amps, obviously no where near enough to blow the main 6 - 16 a fuse in the cut out.

Like I say, I'm 99% sure there person installing these has got confused as there isn't a terminal that says "earth" and not connected it. In some instances there are cables from the main earthing stud flapping around in the enclosure as if they should be connected. I just want to be sure as I've found 10 of these in a row with the same fault. I work all over the UK and all the other shelter manufacturers, and the way I wire street lamps all have earth cables back to the cut out.

The live conductors are then connected to double pole RCBO's, most of which are covered in crap and don't trip when pressed or tested, and even if they do well over stated tripping times.

Thanks for your input in advance,

Rich

Here's a picture of one, with the earth lead loose.

https://www.dropbox.com/s/0j2r84n873x75dv/shelter.JPG


shelter.JPG
 
Send a written report to your supervisor outlining your concerns. If you are there to upgrade the signs and the electrical installation is not your responsibility that is. If you are there to inspect the electrical installation, then you could connect the earth up, but still report your findings initially and obtain an instruction to make the installation safe, as it may be billable to the installing contractor.
 
Hi Voltz,

Thanks for your reply. I'm not mad does that sound bad to you? I'm going to go back to the company with the findings, just wanted to double check with people on here first. Worst case scenario there is a perfectly logical explanation and I'm wrong but it doesn't sit right with me.

Thanks mate,

Rich
 

Reply to Dodgy Bus Shelter Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
267
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
952
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
672
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock