That's going to be a fun one. Are you putting in new 25mm flexi tails?To add more info to the post I made yesterday.
I have a 100A cutout (confirmed as 100A by DNO as they put in an isolator for me in Dec) which feeds in to the property on 16mm tails (25mm to meter and 25mm to isolator then 16mm in)
This leads to a upfront 80A 30mA RCD. Which feeds the main board.
Then there is a feed from the RCD to a Henley block which feeds the board below and that has a 80A 100mA RCD switch and the sockets, cooker and 1 of the showers is on this board.
Then there is a second set of tails jammed into the top of the 100mA RCD feeding the third board on the bottom left which has a 40A 30mA RCD switch.
I’ve put the first pic on again to make it easy to see what I’m describing.