DC colours are either brown and blue or grey and blue dependant upon polarity.
CEF only do Grey & Blue. I ended up buying direct from Cleveland Cable who do all the standard colours.
As an aside a lot of DNO/suppliers don’t allow the use of tri-rated cables as their equipment terminals aren’t designed for fine stranded cables even with ferrules.
Useful to know. What are the issues ?
 
Useful to know. What are the issues ?
Ferrules are only made of very thin material and most DNO/suppliers terminations are designed for the thicker stranded cables, at a guess the screws damage the ferrules allowing fine conductors to splay out causing loose connections. Also the ferrule slightly increases the size of the conductor so some may be very tight to get in without 'modification'.
 
at a guess the screws damage the ferrules
That shouldn't happen - if it does then the screws would also damage thicker stranded cable as well. The screws should have a flat end, which won't be a problem unless done up by a gorilla on steroids - something which would damage the thicker strands as well, if not more so.
allowing fine conductors to splay out causing loose connections
Nope. The ferrule should still contain the strands even if you cut a round hole in it with a badly formed screw. There's a risk of cutting strands, but then the loss of a small number of fine strands would have a proportionately smaller effect on the cable than cutting strands on a 7 or 19 strand cable.
Also the ferrule slightly increases the size of the conductor so some may be very tight to get in without 'modification'.
Now that I have met. Found the hole in the CU earth bar was a "snug fit" for an uncrimped 16mm ferrule, but a crimped ferrule had to be "carefully adjusted" to fit in it.

So basically the arguments come down to :
"Makes the cable too big" which could be valid, except doesn't most of this stuff now come designed to take something like 35mm cable ?
The terminal design/manufacture is defective :mad:

A while ago I tried to search for such restrictions and couldn't find any. The only reference I could find in any DNO documentations related to (IIRC) earth connections in substations where the minimum strand size was 2mm.
 
Mind you, at our church we had the opposite problem - the meter fitter must have left his 'driver at home because he didn't tighten any screws :eek: I'm quite serious, it's a good job some connections weren't heavily loaded.
There were tails into one of the isolators held in by gravity. And a neutral held into both the meter and a henley just by virtue of it being stiff - and he didn't get all the strands in at one end either. The DNO engineer who'd come out to answer my enquiries regarding supply characteristics was "unimpressed" - you could move every cable in it's terminations and we spent a while doing them all up before he put the fuse back and re-sealed everything.
 
Here's a quality install... discovered this after turning off what I assumed were the lights for a couple of fitting changes only to find they were still live.

Dodgy trade pictures for your amusement! - 1 Million Views! IMG_20200611_141334569 - EletriciansForums.net

Lights on a 32A breaker. Clearly whoever did this lacked even the most basic of understanding. Big knockout opened on the top surface as well.

Rented property, young family with kids. Unsurprisingly no stickers, no circuit schedule, no labels... nothing. This is the worst one I've seen. Client also asked me to look into why the two way switching wasn't working... my guess would be the same clown worked on them and screwed it up.
 
Right.... we’ve got excess copper showing at the terminals, holes knocked out for no reason... tails entering 2 different holes....
Second rcd not in use. (What have they done there? Chopped the pins off the bus bar?)

At least it’s a metal board, and they’ve managed to keep all the breakers the same manufacturer.
 
Love the way they’re using the middle RCD as a blanking module. Live and neutral tails going through separate un-grometted / glanded knockouts in metal box.
 
Hard to tell, but looks like the unused RCD has L & N outputs fed from the busbar?

Just possibly the installer didn't know what to do about that (hopefully not after having blown the house service fuse!), and rather than cut the busbar, thought it safer to just remove the N connections to/from the RCD?

At least the N cable with the crimped terminal waving around near the busbar has some tape over it for now - until the tape ages and peels or falls off …
 
All the bits are there to fix this board up. Apart from a few blanking grommits.
The busbar appears to be able to be cut, or snapped apart to feed the right hand side split... Swap some of the breakers around to share across the 2 RCD's and connect the RCD's up with the internal wires that are there taped up. Theres 16 and 6 amp mcb's for the lights.
Im thinking now the busbar hasnt had any pins taken off, and its connected to the outgoing side of the rcd. Dont know if that can damage the rcd or not.
Busbar needs its insulating cover though.

Wiska gland for the tails, just need to drill out one of the holes to make it bigger.... I see an isolator i think.. makes job a little easier.

I see another set of tails... where are they going?
 
I thought it was one of my better efforts.....

when you were 4, before you went to specsavers and using an ivory (ie: 'Insulated') handled knife as a screwdriver. ;-)

[automerge]1592062461[/automerge]
Sparkychick - can you name and shame to the 'authorities'? It looks recent.
 
Last edited:
a beautiful work of art... is there neutrals connected to the earth bar there and floating earths... presumably this was causing a few trips ... now and then . Absolutely atrocious.
 
I missed the busbar going right across, I couldn't understand why the cables to the 2nd RCD were taped up. That's incredible!!!1!!
 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock